running electric under mobile home

70K views 8 replies 6 participants last post by  Psalm91  
#1 ·
i have just bought a used mobile home and i have to run the electric from the electric box on the pole to the electric box in the mobile home. my question is can i use the gray pvc conduit above ground under the trailer and mount the conduit to the frame?

2 threads on same issue merged
 
#3 ·
You will find this at Article 550.15 (H) Exception of the NEC.

(H)​
Under-Chassis Wiring (Exposed to Weather).

Where outdoor or under-chassis line-voltage (120 volts,
nominal, or higher) wiring is exposed to moisture or physical
damage, it shall be protected by rigid metal conduit or
intermediate metal conduit. The conductors shall be suitable
for wet locations.​
Exception: Type MI cable, electrical metallic tubing, or
rigid nonmetallic conduit shall be permitted where closely​
routed against frames and equipment enclosures.
 
#8 ·
Metal Conduit



Hey guys, correct me if I'm wrong, but to me this citation of NEC indicates that cables running 120V or higher must be protected by rigid METAL conduit or intermediate METAL conduit. The question asked specifically asked about installing 120V cables in PVC conduit. Is this not a discrepancy? I'm not trying to be a smart Alec, I'm asking because I'm planning a similar installation with exception that the 120V cables will be installed tight to frame of my truck chassis.
 
#6 ·
Just to clarify. You cannot run direct burial cable under a mobile home with PVC sleeved down at the mobile home panel and the pedestal. That is how they do it here. I have never done a mobile home and never will. But I cannot see any reason you could not do what I suggest. Conduit down - direct burial cable underground - Conduit up? Article?
 
#7 ·
Just to clarify. You cannot run direct burial cable under a mobile home with PVC sleeved down at the mobile home panel and the pedestal. That is how they do it here. I have never done a mobile home and never will. But I cannot see any reason you could not do what I suggest. Conduit down - direct burial cable underground - Conduit up? Article?
Why? please give articles.