Running Electric Under Mobile Home - Electrical - DIY Chatroom Home Improvement Forum
Old 05-07-2010, 03:35 PM   #1
i have just bought a used mobile home and i have to run the electric from the electric box on the pole to the electric box in the mobile home. my question is can i use the gray pvc conduit above ground under the trailer and mount the conduit to the frame?
2 threads on same issue merged
brianbrianj is offline   Reply With Quote
Old 05-07-2010, 03:51 PM   #2
Inspector/Instructor
codeone's Avatar
Yes the NEC allows you to run PVC pipe for electrical tight to the frame under a Mobile home. Any wiring under a mobile home is required to be run in pipe. If its not tight to the frame it has to be buried 18".
codeone is offline   Reply With Quote
Old 05-07-2010, 03:59 PM   #3
codeone's Avatar
You will find this at Article 550.15 (H) Exception of the NEC.
(H)
Under-Chassis Wiring (Exposed to Weather).
Where outdoor or under-chassis line-voltage (120 volts,
nominal, or higher) wiring is exposed to moisture or physical
damage, it shall be protected by rigid metal conduit or
intermediate metal conduit. The conductors shall be suitable
for wet locations.
Exception: Type MI cable, electrical metallic tubing, or
rigid nonmetallic conduit shall be permitted where closely
routed against frames and equipment enclosures.
Old 05-07-2010, 08:01 PM   #4
retired elect/hvac/plumb
plummen's Avatar
Location: south east of omaha/The island of misfit contractors
Rewards Points: 2,020
as long as its strapped supported under trailer it should be fine,between trailer and pole id bury the pipe depending on how far it is
plummen is offline   Reply With Quote
Old 05-07-2010, 08:12 PM   #5
Electrical Contractor
jbfan's Avatar
Rewards Points: 232
That question was answered by codeone here.
running electric under mobile home
Old 05-09-2010, 11:09 AM   #6
Rewards Points: 80
Just to clarify. You cannot run direct burial cable under a mobile home with PVC sleeved down at the mobile home panel and the pedestal. That is how they do it here. I have never done a mobile home and never will. But I cannot see any reason you could not do what I suggest. Conduit down - direct burial cable underground - Conduit up? Article?
Old 05-09-2010, 04:49 PM   #7
codeone's Avatar
Why? please give articles.
Old 10-26-2014, 03:15 PM   #8
Rewards Points: 4
Metal Conduit
(H)
for wet locations.
Hey guys, correct me if I'm wrong, but to me this citation of NEC indicates that cables running 120V or higher must be protected by rigid METAL conduit or intermediate METAL conduit. The question asked specifically asked about installing 120V cables in PVC conduit. Is this not a discrepancy? I'm not trying to be a smart Alec, I'm asking because I'm planning a similar installation with exception that the 120V cables will be installed tight to frame of my truck chassis.
Psalm91 is offline   Reply With Quote
Old 10-26-2014, 03:16 PM   #9
Rewards Points: 4
Oops
I missed the exceptions sorry guys. Thanks!
Replacing Mobile Home Package AC Unit jack roscoe HVAC 3 05-24-2010 03:13 PM
running electric from house Tradesman14 Electrical 3 01-14-2010 12:16 PM
Floor Reinforcing in Mobile Home .. Who do I call? bestshooter Flooring 3 10-03-2009 04:41 PM
piers for a mobile home artbean Building & Construction 4 08-21-2009 08:59 PM
Requirements for running wire under mobile home? MikeVila Electrical 9 11-03-2008 09:41 AM