So you have options, Get a Manometer learn howto use it or Hire someone to check and adjust the Valve. You may have other problems other than the gas valve.
Mmm, well if it came down to it i would definitely buy a manometer before calling a technician... i'm just trying to see if its possible to troubleshoot this issue without one first. Thanks for the input.
How old is this furnace? Are you sure the heat exchanger is ok? Why was the gas valve replaced?
You need to know manifold pressure when doing any adjustments to the burner. You also need to know the delta T over the furnace to understand if its overfiring.
21 years old Rheem RRGG-10E37JKR.
Gas valve was replaced because the furnace wouldn't light. With the help of others and some internet research i used a multimeter to test components that pointed to the gas valve as the culprit. Ordered a used one and the furnace worked again, but with the rollout switch/orange flame issue that i described above.
While replacing the valve i found a large crack in one of the heat exchangers. I dismantled the entire unit and removed all 4 exchanger cells to inspect. 1 was cracked, the rest appeared okay. Replaced the cracked cell and reinstalled/sealed everything.
Thanks for the input.
Meter clocking will tell you how much it is firng. Was there any other appliances running at the same time ie: water heater, clothes dryer, range? Those can screw up your readings.
Is that a new valve or some used item you got from EZ Bay? Don't look new to me. If it is used it may be damaged and you are wasting your time. You cannot adjust a gas valve down or up very far and certainly not as much as your over fired readings indicate.
The proper procedure is to use a manometer to set it but in theory meter clocking will tell you the firing rate. It is NOT the proper way to adjust the valve or a shortcut.
Did you use the proper meter clocking chart and dial and scale. It is easy to make a mistake. You also need to be very accurate with the # of seconds and use a digital watch or stopwatch. I usually do 3 tests and average them.
Great input here, thanks!
There were no other applications using gas. Yes i did 3 runs each time with a digital stopwatch, and averaged them... and then double checked my calculations. All of my readings were 118-120k no matter which way i adjusted the screw.
Yes, the valve was purchased used and i was afraid that that might be the issue as i thought i should be able to see some fluctuation as i adjusted the pressure. I guess i should have been more direct with my initial question, because i guess what i ultimately need to know is whether or not the pressure adjustment is broken on this valve. It seems that it is to me. I was still in troubleshooting mode, though, and just wanted a quick answer about the reducing pressure thing and wanted to keep it brief... whoops. :whistling2:
Thanks again for the input everyone.
edit: and if this discussion is beyond the scope of what this forum is intended for, just let me know. no worries.