I bought a Duromax xp12000eh portable generator (Rated Gas-9500w/Surge Gas-12000w, Rated Propane-9025w/Surge Propane-11400w) in hopes of running my entire house if needed. 50amp inlet box was installed and wired to the main panel with a 50amp breaker. Not using a transfer switch. Several weeks ago my son and I went through the house and each breaker with a clamp meter to measure amps. After yesterdays test run with the generator and testing numerous appliances at the same time, I am happy with the generator to power my home.
Now comes the central AC. It is a 5 ton Amana ASX16 single speed scroll compressor that was installed June 2018 with a Goodman air handler. Clamp meter read 49amps on start during my testing with a LRA rating of 135. I installed a 5-2-1 kit which brought the startup down to roughly 34amps.
I tested the AC by itself under generator power using propane with every other breaker off. The generator stumbled slightly once but recovered rather quickly. I noticed the AC compressor sounded different at startup and the fan had roughly a 2 second delay to start VS starting almost instantly while running off normal power. Also, while running on generator power, it appears the fan was not running at fun speed and there was a vibration coming from the unit that would cause the grate to make a noise. You can hear all this in the videos.
I read another post about testing the frequency but unfortunately that was after the fact :gah: ....and if that's where I need to start I will have to hook the generator back up.
Generator Start
Normal Start
Now comes the central AC. It is a 5 ton Amana ASX16 single speed scroll compressor that was installed June 2018 with a Goodman air handler. Clamp meter read 49amps on start during my testing with a LRA rating of 135. I installed a 5-2-1 kit which brought the startup down to roughly 34amps.
I tested the AC by itself under generator power using propane with every other breaker off. The generator stumbled slightly once but recovered rather quickly. I noticed the AC compressor sounded different at startup and the fan had roughly a 2 second delay to start VS starting almost instantly while running off normal power. Also, while running on generator power, it appears the fan was not running at fun speed and there was a vibration coming from the unit that would cause the grate to make a noise. You can hear all this in the videos.
I read another post about testing the frequency but unfortunately that was after the fact :gah: ....and if that's where I need to start I will have to hook the generator back up.
Generator Start
Normal Start