Hi,
I attempted to install a Honeywell RTH2510 digital thermostat as a Christmas present for my girlfriend. I have read the manual multiple times, labeled all wires and according to the manual, I believe I have everything hooked up correctly. However, as soon as I turn the breaker on, the unit begins running even with the tstat turned to the off position and the fan in the auto position. Here's details:
Old tstat (White-Rodgers LR27935 Class 2 - Type 1f58-34):
Orange - O
Yellow - Y
Red - R
Green - G
Blue - W2
Brown - C
White - E
Black - L
New tsat:
Orange - O/B
Yellow - Y
Red - R
Green - G
White and Blue - W/Aux (The manual says 'If your old thermostat had E and Aux wires connect both wires to AUX terminal)
Brown and Black have been taped off.
Additionally there are two jumpers:
JP1 is set to HE (The manual says to do this if you have connected a wire to the G terminal and have an electric furnace)
JP2 is set to O (The manual says to do this if you have a heat pump and have O wire connected to the O/B terminal)
I don't know much about heat pumps (where I'm from we used swamp coolers!) so forgive me if my terminology is incorrect.
When I turn the breaker on with the faceplate of the tstat removed, the blower inside is running, but nothing outside is running and I feel air coming from the vents. It does the same thing with the faceplate installed with the heat/cool switch set to off and the fan switch set to auto.
When I turn the heat/cool switch to heat and raise the temperature setting, the tstat display says 'heat on' and the inside blower runs but the outside unit does not.
When I turn the heat/cool switch to cool and lower the temperature setting, the tstat display says 'cool on' and both the inside and outside units are running and cold air comes from the vents. When I raise the temp setting, the outside unit stops but the inside unit keeps running.
One last piece of info, when I first turned it on after hooking it up, there was a clicking sound (sounded like a relay) coming from the outside unit that clicked every few seconds and then stopped. It has not done this since.
Link to installation manual: http://customer.honeywell.com/Honeywell/getliterature.axd?LiteratureID=69-2380ES.pdf
Thank you in advance for any help you might provide!
I attempted to install a Honeywell RTH2510 digital thermostat as a Christmas present for my girlfriend. I have read the manual multiple times, labeled all wires and according to the manual, I believe I have everything hooked up correctly. However, as soon as I turn the breaker on, the unit begins running even with the tstat turned to the off position and the fan in the auto position. Here's details:
Old tstat (White-Rodgers LR27935 Class 2 - Type 1f58-34):
Orange - O
Yellow - Y
Red - R
Green - G
Blue - W2
Brown - C
White - E
Black - L
New tsat:
Orange - O/B
Yellow - Y
Red - R
Green - G
White and Blue - W/Aux (The manual says 'If your old thermostat had E and Aux wires connect both wires to AUX terminal)
Brown and Black have been taped off.
Additionally there are two jumpers:
JP1 is set to HE (The manual says to do this if you have connected a wire to the G terminal and have an electric furnace)
JP2 is set to O (The manual says to do this if you have a heat pump and have O wire connected to the O/B terminal)
I don't know much about heat pumps (where I'm from we used swamp coolers!) so forgive me if my terminology is incorrect.
When I turn the breaker on with the faceplate of the tstat removed, the blower inside is running, but nothing outside is running and I feel air coming from the vents. It does the same thing with the faceplate installed with the heat/cool switch set to off and the fan switch set to auto.
When I turn the heat/cool switch to heat and raise the temperature setting, the tstat display says 'heat on' and the inside blower runs but the outside unit does not.
When I turn the heat/cool switch to cool and lower the temperature setting, the tstat display says 'cool on' and both the inside and outside units are running and cold air comes from the vents. When I raise the temp setting, the outside unit stops but the inside unit keeps running.
One last piece of info, when I first turned it on after hooking it up, there was a clicking sound (sounded like a relay) coming from the outside unit that clicked every few seconds and then stopped. It has not done this since.
Link to installation manual: http://customer.honeywell.com/Honeywell/getliterature.axd?LiteratureID=69-2380ES.pdf
Thank you in advance for any help you might provide!