Hi All,
I've read through some older posts on Multi Wire Branch Circuits. Several of these older posts explain that you should use a double pole breaker or tie the breakers together to ensure they are not on the same phase. Part of the reason is to make sure that if one breaker is off and the other is left on, that there isn't a potential for shock at the devices that use this wiring.
My question about protecting the circuit is from overload. My understanding is that if you share the neutral across two single pole breakers, you have the potential for overloading the neutral without actually tripping either breaker. E.g. On two 15 amp breakers, you could have 10 amps running on each circuit, thus bringing back more than 15 amps on a 14 awg neutral wire and possibly causing a fire.
1) Is there truly a concern of overloading if you use a shared neutral across two single pole breakers?
2) Will using a double pole 15 amp breaker fix this potential hazard?
Thanks
John
I've read through some older posts on Multi Wire Branch Circuits. Several of these older posts explain that you should use a double pole breaker or tie the breakers together to ensure they are not on the same phase. Part of the reason is to make sure that if one breaker is off and the other is left on, that there isn't a potential for shock at the devices that use this wiring.
My question about protecting the circuit is from overload. My understanding is that if you share the neutral across two single pole breakers, you have the potential for overloading the neutral without actually tripping either breaker. E.g. On two 15 amp breakers, you could have 10 amps running on each circuit, thus bringing back more than 15 amps on a 14 awg neutral wire and possibly causing a fire.
1) Is there truly a concern of overloading if you use a shared neutral across two single pole breakers?
2) Will using a double pole 15 amp breaker fix this potential hazard?
Thanks
John