Hola all. So I was initially intending to hire an electrician for this, but for $2400, I started wondering if it wasn't something I could do myself. Now I know a lot of you on this forum are electricians, and I appreciate the insight, so let me know your thoughts as I outline my plan - and if I'm missing anything. I have my thoughts listed below, and then following my questions.
Here's the plan: From my 100 amp panel, run a line underground 30' to my detached garage.
Here's the process:
1) 50 amp 2 pole breaker on the main panel (from the data cards on my equipment, I assume the max I could possibly use at any given time would be 46 Amps)
2) Run 2 hots from the breaker, 1 neutral (4 gauge THNN), 1 ground (6 gauge solid), from the main in sched 80, 1.25" (above ground) PVC underground. run these wires the 30' in sched 40 (below ground), and back up in sched 80. Through the outer garage wall using an access body and into the garage.
3) bring it up in sched 80 PVC to the sub panel.
4) using a 100A sub (for the space and future proofing - I may upgrade to a 200a main in the future as well) with 8 spaces connect the 2 hots, neutral and ground.
5) and then run the circuits in my garage from there - lights, tools, 220 for some tools, etc.
Additionally, not one of the 5 electricians I got quotes from stated that a ground rod was required - and I did ask. However, on this forum, I have seen that basically everyone recommends a ground rod for a separate structure. So I need some insight on this. Now here's my questions:
1) is a 50 amp breaker the correct size based on the max I calculated from the data cards on my equipment? should it be 60?
2) I believe the wire size and PVC size (1.25")is correct - thoughts?
3) Would it be sufficient to ground the sub to the water lines that in the same structure. These water lines exit the garage, are buried 18" below ground, and then to the house. If not, please provide advice on what I would need for a grounding rod (I have no experience with a ground rod).
4) am I missing anything else for this project?
5) What are thoughts on why I would hire this out instead of completing on my own?
As always - all insight is appreciated. I really rely on the feedback from this forum, and have been able to accomplish a lot - so thanks.
J
Here's the plan: From my 100 amp panel, run a line underground 30' to my detached garage.
Here's the process:
1) 50 amp 2 pole breaker on the main panel (from the data cards on my equipment, I assume the max I could possibly use at any given time would be 46 Amps)
2) Run 2 hots from the breaker, 1 neutral (4 gauge THNN), 1 ground (6 gauge solid), from the main in sched 80, 1.25" (above ground) PVC underground. run these wires the 30' in sched 40 (below ground), and back up in sched 80. Through the outer garage wall using an access body and into the garage.
3) bring it up in sched 80 PVC to the sub panel.
4) using a 100A sub (for the space and future proofing - I may upgrade to a 200a main in the future as well) with 8 spaces connect the 2 hots, neutral and ground.
5) and then run the circuits in my garage from there - lights, tools, 220 for some tools, etc.
Additionally, not one of the 5 electricians I got quotes from stated that a ground rod was required - and I did ask. However, on this forum, I have seen that basically everyone recommends a ground rod for a separate structure. So I need some insight on this. Now here's my questions:
1) is a 50 amp breaker the correct size based on the max I calculated from the data cards on my equipment? should it be 60?
2) I believe the wire size and PVC size (1.25")is correct - thoughts?
3) Would it be sufficient to ground the sub to the water lines that in the same structure. These water lines exit the garage, are buried 18" below ground, and then to the house. If not, please provide advice on what I would need for a grounding rod (I have no experience with a ground rod).
4) am I missing anything else for this project?
5) What are thoughts on why I would hire this out instead of completing on my own?
As always - all insight is appreciated. I really rely on the feedback from this forum, and have been able to accomplish a lot - so thanks.