I have a GMVC95 furnace that went out with a E6 code - (Low Pressure Switch contacts closed or short in wires). Low fire would ignite but went out after a short time. Troubleshooting revealed no short in wires and switch operated but with very little suction applied. I thought 'weak spring?' and found what looked like a square adjustment screw on the back of pressure switch. Test of 1/4 turn counterclockwise - no change. Test of 1/4 turn clockwise resulted in furnace operating normal - 3 days now. I think this adjustment tightened up the spring so the switch would not close too soon but I do not know if the adjustment is correct or safe to leave the house for a week. Do I leave it as is, pay a HVAC company to check it or go ahead and replace it with a new unit from Goodman?