Dual Zone Mini Split - Vacuum/Charge Lines

1 reading
3.8K views 9 replies 4 participants last post by  roughneck  
#1 ·
Building a new shop and purchased a Cooper & Hunter Dual Zone Mini Split. I have set up several Mini Splits in the past in a field setting (Iraq) and all seemed to work fine (considering the environment). These were all single zone units so I have never vacuumed and charged a dual zone unit. Provided instructions are sufficient but I cannot find any clear indication about vacuuming and charging the lines (pre-charged unit). I believe both lines are vacuumed, tested and charged separately as if two single zone units. Can someone clarify that for me? I don’t want to charge one line, then vacuum the second only to suck out all the refrigerant from the 1st line.

Thanks
Image

in advance for any assistance And advice.
 
#6 ·
Cooper & Hunter seem to have good reviews, not the cheapest model but not the most expensive either… all the ones I set up in Iraq were Mitsubishi. Pretty easy to set up and gave me something to do between requirements. I’m 98% certain the lines are set up separate but it’s the 2% that always get me in trouble. Could hire an HVAC guy to do it but, to be honest, not interested in paying hundreds of dollars to a guy to hook up a vacuum pump, gauges and nitration bottle then stand around for 2 hours when I stand around just as easily and not have to pay outrageous amounts.
 
#9 ·
I would get ALL the lines done and tested and vacuumed to >100 microns before I opened the valve where the charge is. Make darned sure that the total length of piping is less than the charge in the compressor.