Can I put 2 #6 current carrying wires with a #8 ground into an existing 3/4” metal flex conduit that already has 2 #8 current carrying wires with a #10 ground? Total of 6 wires.
The voltage drop requirement in the NEC was changed recently.For <=60A wire, #10 ground will suffice unless the reason you are using larger wire is voltage drop for long distance. Anytime you upsize the conductors for voltage drop, you must upsize the ground in proportion.
There is a conduit fill rule but there is also a max number of CCC (Current Carrying Conductors) per conduit (regardless of conduit size) before you have to derate.Can I run the following wires through 3/4" EMT?
2 #6 THHN, for an EVSE;
2 #12 THHN for a GFCI receptacle;
4 #14 THHN for a 3-way light switch?
This list includes a neutral for each of the two 120V circuits.