There is another ongoing thread about CCC and derating but I don't want to hijack that thread for my situation. I basically would like someone to set me straight on these rules.
I have an existing 3/4" EMT conduit between junction box A and junction box B. A to B is 25 feet apart. How many 20A #12 THHN conductors can I put in it?
The conduit fill table says 16. But the real limit is really how many CCC there instead.
My understanding is I can have up to 9 #12 CCC before derating down to 15A, is this correct? If so then that means maximum of four 20A circuits with 4 hots and 4 neutral total of 8 CCC. However, if I use MWBC then I can squeeze in six circuits with 6 hots and 3 neutrals?
Are there exceptions whether those CCCs if some of them are impossible to be energized at the same time?
For example, in a 3 or 4 way wiring, if I have multiple travelers but only one can be engergized at one time, do all travelers count as CCCs?
Another example, if I have a switch leg then the hot and the switched leg are both CCCs, no doubt, but since we are now required to run a neutral to the switch box, but that neutral is not used or even connected, does that neutral count as a CCC because one day in the future it may be used as one by someone else?
Thank you for your time.
I have an existing 3/4" EMT conduit between junction box A and junction box B. A to B is 25 feet apart. How many 20A #12 THHN conductors can I put in it?
The conduit fill table says 16. But the real limit is really how many CCC there instead.
My understanding is I can have up to 9 #12 CCC before derating down to 15A, is this correct? If so then that means maximum of four 20A circuits with 4 hots and 4 neutral total of 8 CCC. However, if I use MWBC then I can squeeze in six circuits with 6 hots and 3 neutrals?
Are there exceptions whether those CCCs if some of them are impossible to be energized at the same time?
For example, in a 3 or 4 way wiring, if I have multiple travelers but only one can be engergized at one time, do all travelers count as CCCs?
Another example, if I have a switch leg then the hot and the switched leg are both CCCs, no doubt, but since we are now required to run a neutral to the switch box, but that neutral is not used or even connected, does that neutral count as a CCC because one day in the future it may be used as one by someone else?
Thank you for your time.