Arc fault breaker tripping

3.2K views 16 replies 6 participants last post by  DanS26  
#1 ·
Hi,

This is a new built home which passed the rough-in inspection and I am getting ready for the final but I have one Arc Fault breaker the is tripping which I need to address before the inspector comes.

A bit of background. I installed all of the switches, plugs, and lights sometime in April 2023 and I had no issues with anything until about a months ago where one of the 15 amp circuit on an arc fault was tripping. I unplugged everything from the circuit but it was still tripping after a short period of time (1-5 minutes). I tested the break with the "test" button which worked as it should. I than pushed on the breaker to make sure it was well seated in the panel and that seem to do the trick.
I plugged back the few things that were on the circuit (radio, electric recliner and a laptop power cord) and no issues for about three weeks until yesterday when it randomly tripped again when I plugged in my laptop to charge it. The weird thing about this is I have my Christmas tree lights plugged into this circuit and my radio and it doesn't trip the circuit. It's only went I plug in something like my laptop power cord or a fan that I was using to test things.

Today open all 11 receptacles on the circuit to make sure the screws were tight and the marettes were tight but found no issues. I switched out the breaker with another arc fault break but that did not solve the issue. The panel is a 200 amp Square D with plug on neutral.


At this point I am at a lost as to why this breaker is tripping and I can't seem to find a pattern either. Does anyone have suggestion or insight?

Thank you,
Arnold
 
#4 ·
Many arc fault breakers give a code a to what made the breaker trip. Do a search for your type of breaker to see how to interpret the code.

From your list of loads on the circuit it doesn't sound like an overload. Arc fault breakers don't like some motors so your fan may be causing the trip. The transformer in your lap top may also be causing the trip problem.
 
#5 ·
Many arc fault breakers give a code a to what made the breaker trip. Do a search for your type of breaker to see how to interpret the code.

From your list of loads on the circuit it doesn't sound like an overload. Arc fault breakers don't like some motors so your fan may be causing the trip. The transformer in your lap top may also be causing the trip problem.
I was aware some motor and electronic device don't work well with arc fault breaks but I thought all current version of those breaker had address that? What I find odd is that none of my other arc fault circuit have had issues tripping while using a laptop power cord or a fan. IT's just that one circuit.

I'll try to dig up the code for my breaker and see what I can figure out from that.

Thanks,
Arnold
 

Attachments

#7 ·
My Square D QO breaker have what they call the Time Saver Diagnostics which I tested all of my arc fault breakers. The circuit in question triggered right away but to my surprise, the circuit above it which is for the utility/laundry room also trigged right away. I never had any issues with it that circuit and it run the dehumidifier and two boot/mitten electric drier.

Trips instantly (less than one second)
Fault to Ground
• Arcing to ground
• Shared neutral
• Grounded neutral
• Ground fault

Arnold
 
#9 · (Edited)
So is this an accurate summary?
  • The circuit has operated normally for 7 months with a variety of things plugged in but started tripping in the last month.
  • You’ve tried two different breakers.
  • The breakers trip even if nothing is plugged into a receptacle.
  • You’ve checked all the receptacles (we assume only receptacles) for loose screwed connections (not back stab) or marrettes.
You would have had to check the black and white wire connections to the breaker when you swapped breakers (since its a plug-on neutral panel), but have you checked the ground connection for that cable?

Since the house seems to be still under construction, has there been any work done along the routing of the cable where a screw or nail could have damaged it?
 
#10 ·
So is this an accurate summary?
  • The circuit has operated normally for 7 months with a variety of things plugged in but started tripping in the last month.
  • You’ve tried two different breakers.
  • The breakers trip even if nothing is plugged into a receptacle.
  • You’ve checked all the receptacles (we assume only receptacles) for loose screwed connections (not back stab) or marrettes.
You would have had to check the black and white wire connections to the breaker when you swapped breakers (since its a plug-on neutral panel), but have you checked the ground connection for that cable?

Since the house seems to be still under construction, has there been any work done along the routing of the cable where a screw or nail could have damaged the cable?
That's pretty accurate except the problem went away after about 24-48 hours after the first time around without really figuring out what was causing the issue but around three weeks later (right now) the same problem returned.
This time the circuit only tripped when I plugged the laptop power cord or a desk fan in any of the plugs but the breaker wouldn't trip if it was just the Christmas tree light plugged in.

The only thing that was installed was the veneer stone at the back of the wood stove but nothing else, not even the baseboard that I still have to do.

I have not checked the ground in the panel to make sure that's all good but just like three weeks ago, the problem has disappeared. I can now plug in multiple laptop and run the desk fan on that circuit at the same time without any issues.

Arnold
 
#12 ·
That is what I thought but it I've tried different laptop and its own power cord with the same result. Also using a regular five year old desk fan would also trigger the breaker.

The issue is for the second time now the problem has disappears after about 24 hours without known why and what caused the "fix". Could the generator panel be causing this random issue if not properly wired or the heat pump furnace surge protector?


Arnold
 
#16 ·
That was for the first time this whole thing occurred about a month but granted I did not have the Christmas tree lights install or something of low power consumption plugged-in that circuit at that time. The second time around it was not an issue but I am not sure if LED have such a low power draw that it didn't affect anything compared to a fan or a charging laptop with a bigger load!
In terms of construction, nothing has been done to those wall since drywall except for the veneer stone behind the wood stove that was done at the begin of July 2023.
  • Why would the circuit just random trip only when there is a bigger load on it but not when there is either nothing or very small load?
  • Why does it all of a sudden "disappear" and everything goes back to normal?
Thank you,
Arnold
 
#17 · (Edited)
Look for a neutral/ground bond somewhere on the circuit. Take every device out and look for white wire touching or barely touching the bare ground wire. It seems to take a heavier load to trip the breaker thus you have an intermittent problem to run down. Take apart every fixture, outlet, etc. to find the fault. It could be as hard as finding a drywall screw making the bond. Lots of possibilities.

After taking the circuit apart and before connecting anything.....close the breaker.....does it hold. If yes start reassembling the circuit one at a time from the breaker on out each time checking for a trip by putting a load at each location.

Good luck.