OK, so cost is an object. Aluminum is your friend even if you've been told lies about it. Aluminum at these large sizes is proven as safe as copper, not least because the lugs it'll be landing on
are made of aluminum because aluminum lugs are a winner.
The "it's underground" logic is dumb. That only matters if the insulation is pierced by rocks (which means you didn't line the hole with a good width of fine dirt/sand on each side of the wire). If your insulation is pierced, wire metal
will be the least of your problems!
Sure,
if cost is no object.
Figure 2-3x the cost for copper. Your money, hoss.
Also you know copper wire is a huge target for copper thieves, right?
More "cost is no object" eh?
NEC doesn't care about voltage drop but does say you are not to plan to load the circuit beyond 80% ampacity. In Canada they do care, but apply that same rule to say you calculate the 3% based on 80% of load. 40A in your case.
2/0 AWG aluminum wire ($6/ft for USE-2) will give 2.71% voltage drop at 40A.
4/0 AWG aluminum ($9/ft for USE-2) is 1.95% voltage drop at 40A.
1 AWG copper ($13/ft for USE-2) is 2.47% drop at 40A.
2/0 AWG copper ($20/ft for USE-2) is 1.81% drop at 40A.
I wouldn't normally recommend USE-2 for direct burial, but I needed something I could compare "apples to apples". Normally with AL direct burial you use quadplex URD or MH feeder. Fact is, they don't offer a lot of choice of copper wire designed for direct burial
because nobody does that lol. Anyone silver-spoon enough to bury large Cu usually springs for conduit. That said, I wouldn't, because conduit makes it easy for copper thieves.
I'm assuming ground wires 2 sizes smaller than conductors because of
250.122(B).
No go, can't parallel per 310.10(H).
Don't quit your day job lol. No, you can't do that. NEC 110.3.
Why do you hate aluminum? I bet if you honestly sat down and thought about it, you'd say "SAFETY".
Then why are you proposing all this dangerous nonsense? See you're just all over the place.
Slow down and listen to experts. At the end of the day you want your money not wasted and the project to work. Stick with gold standard practices.
Speaking of safety, using a torque wrench on lugs
is actually important (unlike aluminum). You're gonna use one, right? Aluminum properly torqued is safer than copper "gud-n-tight".
Now you're playing with power! Except I'd scour Craigslist, eBay and Facebook Marketplace for those transformers. They pop up from time to time for a few hundred bucks.
As for wire cost, you're now at 2x #6 aluminum for about $1.50/foot for the 3 wires.
Or #8 copper at $2.50/foot.
Aluminum loses its advantage on small wires since less of the cost is mineral value and more is the cost of the insulation jacket.