400 Amp Service with 2 200 Amp Panels

98K views 52 replies 11 participants last post by  Tom738  
#1 ·
I'm preparing to build a new home that will have 400 Amp service with a main 200 Amp panel and a 200 Amp sub-panel. The home is a long ranch so the main will feed 4 bedrooms, 2 full baths, laundry room and exterior. The sub-panel will be 100' from the main and will feed the kitchen, great room, 1/2 bath and the garage/garage shop. I'm having trouble getting a straight answer on the size of the feeder cable from the main panel to the sub-panel.

What size copper feeder cable will be required between the main panel and sub-panel?

I believe I need a 4 wire feeder cable. Is this correct?

Thanks for your help!
 
#2 ·
You'll get folks to dispute this since one panel is not carrying the entire load, but here even for a 400A service with two 200A panels we would use 4/0AL (2/0CU) to feed each panel.

If using cable then yes, you need two hots, a neutral and a ground. Typical would be SER cable.
 
  • Like
Reactions: Know A Little
#3 ·
Is it against code to have 2 200 Amp panels for 400 Amp service?

Is it recommended to have two 200 Amp services with one feeding each 200 Amp panel? If this were done, wouldn't we need two meters with separate service cables from the utility? This just seems like it would add cost more than anything.
 
#4 ·
Is it against code to have 2 200 Amp panels for 400 Amp service?

Is it recommended to have two 200 Amp services with one feeding each 200 Amp panel? If this were done, wouldn't we need two meters with separate service cables from the utility? This just seems like it would add cost more than anything.
 
#7 ·
I've done a load calculation and I don't need 400 but I need more than 200. My garage shop will have several 240v 30-50 Amp dedicated circuits (table saw, dust collector, welder, electric heater, etc.). I decided on going with 400 as I plan to add a separate Morton building and want to have the ability to add service to the Morton building at that time.
 
#8 ·
But one panel would not be a subpanel off of the other, 200 amp, panel.

Both 200 amp panels would be "main" panels, installed next to each other so the top (main) breakers of both may be flipped off at the same time.
 
#13 ·
If I may summarize...A disconnect will be placed next to the main panel. The disconnect will be fed from the main panel and the sub-panel will be fed from the disconnect. I can have a main breaker in the sub-panel if I want to be able to disconnect power to the sub-panel at the sub-panel. Is this correct? What type of "disconnect" is required in this case?
 
#19 ·
Since I'll have more than 6 breakers in the 2nd panel, I believe I will need a main breaker at the panel in addition to the disconnect at the main panel. Is this correct?

I'm just curious, but is this 2nd panel considered a main panel since it's not coming directly off the SE panel?

What type of disconnect is required/suggested for the 2nd panel?

I really appreciate all of the great information you've provided!
 
#26 ·
A 320/400A meter base with main breakers is quite expensive, so I don't really see any cost savings there. It is simpler to install and cleaner though.
 
#29 ·
All - I really appreciate all of the great information provided here and the very helpful responses. I have decided to go with a 320/400 Meter Base/Combo with 2-200 AMP Breakers along with 2 Main Lug Panels rather than 2 Main CB Panels.

Now, I'm trying to decided on what size main lug panels to go with. I've put together the circuit configuration below. Do I go with 30-30 panels?

Image
 
#36 · (Edited)
My understanding is that AFCI protection is required on all circuits supplying wall outlets.
When the code says outlets, they are talking about any point of use, not "wall outlets". Those are referred to as receptacles or receptacle outlets. So the lighting circuits in the dwelling will require AFCI as well.

The 2008 requirements,

"(B) Dwelling Units. All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sun rooms, recreation rooms, closets, hallways, or similar rooms or areas shall be protected by a listed arc-fault circuit interrupter, combination-type, installed to provide protection of the branch circuit."

I would interpret that to include finished rooms or areas in a basement.

Looking at it the other way, kitchen,bathrooms, laundry and the garage don't need them.
 
#40 ·
When the code says outlets, they are talking about any point of use, not "wall outlets". Those are referred to as receptacles or receptacle outlets. So the lighting circuits in the dwelling will require AFCI as well.

The 2008 requirements,...........
And the 2014NEC goes insane over the top with these requirements, like refers and DW's as well. Pretty much everything in a dwelling.