1 - 4 of 16 Posts
Those units are designed to run a lot. They will modulate the compressor and fan speeds to a point where they maintain the setpoint and hardly every shut off. This is ok because the power usage is very minimal as the units ramp down. Also, if you are using the standard remote control then the temperature sensor is in the unit and in order for it to get a sample of the surrounding air it will run the indoor fan and may not be running the outdoor unit. You can get MHK1 thermostats for the units that will sense the temperature at the wall mounted thermostat instead of at the unit. The MHK1 thermostats can also be set to be programmable to change setpoints at 4 different times during the day.
Your contractor does not know the Mitsubishi product. The room temperature thermistor is in the wall mounted head unit not in the remote. Also, does your indoor unit have an "i-see sensor" that looks like this indoor unit because it will act differently based on the windows in the room and which side of the house the unit is facing. It will also act strangely if the pass through hole behind the unit is not properly sealed and drafts are coming through from the outdoors and offestting the room sensor. I have seen some poor installations where that was the case.
here is you operations manual for a MSZ-FE09NA: http://usa.mylinkdrive.com/uploads/...uploads/documents/208/document/MSZ_FE09-12NA_Operation_Man_SG79F408H02_6-11.pdf
AUTO MODE: The unit selects the operation mode according to the difference between the room temperature and the set temperature. During AUTO mode, the unit changes mode (cool-heat) when the room temperature is 4F away from the set temperature for more than 15 minutes.
8-6. i-see CONTROL OPERATION (MSZ-FE09NA MSZ-FE12NA)
The sensors constantly measure the room and floor/wall temperatures to automatically adjust to the set temperature by estimating the temperature actually perceived by a person inside the room (“sensory temperature”).
Advantages
· The air inside the room is conditioned quickly to a comfortable condition.
· The room will not become too cold or hot even when the air conditioner is kept on
for a long period.
· The air conditioner will not overcool or overheat, which means you can save on electricity.
i-see control operation is activated when i-see button is pressed with a thin stick in manual COOL or manual HEAT mode.
NOTE:
i-see control operation is activated when the remote controller is first used following replacement of the batteries
or resetting of the remote controller.
i-see control operation is cancelled when i-see button is pressed with a thin stick once again.
NOTE:
If the conditioner is turned OFF without cancelling i-see control operation, i-see control operation is activated the
next time the air conditioner is turned ON.
• When AREA setting is not activated, the sensing range of i-see Sensor differs depending on the installation location of
the air conditioner.
Refer to "Remote controller in SERVICE FUNCTIONS".
Taken from the service manual: http://usa.mylinkdrive.com/uploads/documents/215/document/MSZ-FE09-18NA_Service_OBH542_4-11.pdf
You would do yourself a lot of good to read all manuals from the manufacturer.
1 - 4 of 16 Posts