Re: Lennox SLP98 pressure switch issues

The G71 is very similar to the SLP.

Some of them had a issue with cracks in the condensate trap. Very small hairline cracks. That causes them to suck air in there and get airlocked or water to get hung up in the secondary heat exchanger. Also there are tiny o-ring gaskets where it attaches to the furnace which can leak. Plus some people overtightened them to the plastic fitting it attaches to on the furnace and cracked it too. If it is cracked it needs replacing. Must NOT overtighten the screws of the trap to that fitting.

Also that furnace must have a 1/2 inch slope from back to front and 1/4 to 1/2 inch slope sideays towards the condensate trap.

Lennox fixed that issue by putting slope on the mounting of the heat exchanger in later models. I always put a bit of back to front slope on all my installs just to be safe and sure and promote good drainage and it does not hurt anything anyway.

I would replace the trap and it is VERY critical all joints and sources of where air can get in are sealed properly.

Now that you messed with the gasket on the collector box and the inducer you may have air leaks there. Only way to know for sure there is none is to replace those gaskets or seal them with red RTV silicone.

Finicky da*mn furnaces they are.:vs_mad:
 
Where the hoses attach to the collector box ( what you call cold header box ) remove them one at a time and poke a drill bit thru. Some of the G51s and 61s had a problem with mineral building up inside the port. Lennox then bevelled the hole on the next series to fix it but if yours is partly plugged that can trip the switch.

The sloping is very important as some of them get water hanging in the back of the secondary heat exchanger. It needs to slope forward 1/2 and inch and 1/2 an inch towards the trap. Unless you got the series where they did it internally but I don't know the serial # of them. Slope is always helpful.
 