You will never get 400 CFM if you undersize the duct. If you are looking to achieve that CFM then it needs to be vented according to the manufactures specifications, that size and friction need to be considered. You can probably find a fan chart for that fan that will say how much air you will move at a given static pressure.

Considering that, 4” will vent, sure, but you will be very disappointed with the performance and noise. 5” is probably going to have similar results.

Square duct will not cause your any problems, utilize this to your advantage. If CFM or noise is most important to you then you may need to drop your ceiling to get the right vent size through there. You may need to do a combination of both.

Just keep in mind, the smaller you go the less air you will move. There is a big difference between 6” vs 5”. The box only says how much air it will move in its BEST CASE SCENARIO, these are small motors so you need to give them every helping hand you can give them.

Lastly, do not share your bathroom and kitchen exhaust lines... that is not something you want to smell in the kitchen ever! Backdraft dampers will not help you enough here and you may find one vents very poorly or not at all if both fans run together. It’s just a bad idea all over. Don’t do it.