well since Philly is what is old when speaking of electric ...LOL
we have 208 3 phase in the city .. usually high leg b phase
out in the suburbs you see more 240 3 phase all legs 120 to ground:
Psst! The high leg 3 phase is the 240 volt kind (delta system).
The symmetric (wye, all legs 120 to ground) is the 208 volt kind.
Older primary (substation to street) lines may be 4KV (4160 volt) phase to phase or 2400 volts
phase to ground.
In cities, modern primary lines are typically in the 13000 volt phase to phase range, in rural areas they
could run up to 30000 volt phase to phase usually with just one of the three phases serving
each street.
Depending on the pole transformer array, buildings receiving 3 phase power might get either
120/208 or 120/240 volt (secondary) power regardless of the primary voltage.