RESOLVED: Zone valve opens but doesn't fire boiler
I posted two weeks ago regarding this issue, but further testing revealed I didn't have all the facts the first time around.
Four zone heating system. Three of the zones each independently open and call for heat. One additional zone opens, but does not call for heat.
If I set the temp on the malfunctioning zone above ambient temp to fire the boiler, nothing happens UNLESS I do the same with any other zone. Then and only then does heat come to the malfunctioning zone along with the second zone.
I checked the wiring in the junction box that houses the zone/transformer/boiler wiring. Nothing loose.
4 zone gas / baseboard radiators
Burnham Series 2 Model B Gas Boiler
Taco Circulator 007-F5
Honeywell Hydronic Zone Valves (4) V8043E1012
Valve head 40004850-001 Rev. A
I'm leaning towards zone valve malfunction (end switch). Hoping for some corroboration and guidance as to whether I should attempt replacing the head myself. Many thanks.
I posted two weeks ago regarding this issue, but further testing revealed I didn't have all the facts the first time around.
Four zone heating system. Three of the zones each independently open and call for heat. One additional zone opens, but does not call for heat.
If I set the temp on the malfunctioning zone above ambient temp to fire the boiler, nothing happens UNLESS I do the same with any other zone. Then and only then does heat come to the malfunctioning zone along with the second zone.
I checked the wiring in the junction box that houses the zone/transformer/boiler wiring. Nothing loose.
4 zone gas / baseboard radiators
Burnham Series 2 Model B Gas Boiler
Taco Circulator 007-F5
Honeywell Hydronic Zone Valves (4) V8043E1012
Valve head 40004850-001 Rev. A
I'm leaning towards zone valve malfunction (end switch). Hoping for some corroboration and guidance as to whether I should attempt replacing the head myself. Many thanks.