We are rewiring an old house that is built on 2.5" x 1.5" lumbar so, we can not staple the NM to the stud and maintain 1.25". We are using stand off's and zip tying the NM to the stand off. I am concerned that the zip tie will pinch the NM too much. The stand off's are 300.4(d) compliant, but are they 334.30? Attached a cell picture. What do you think? Thanks
 

Attachments

· Registered
Joined
·
3 Posts
Discussion Starter · #4 ·
Lol... no crack here.. No, I am concerned about the edge of the zip tie cutting the sheathing of the NM. The ties have a bit of a "corner" on them and they must be tied at an angle (see picture). I guess the money question is, if you were an inspector would you consider it secured per 334.30? Thanks again.
 

· Registered
Joined
·
1,013 Posts
Why do you even need zip ties if the standoffs are rated and listed for the purpose of securing the NM cable? What do the installation instructions for the standoff say? I'm sure it doesn't say to use a zip tie to secure the NM to the standoff....
 

· DIY'r
Joined
·
523 Posts
If you really wanted to be anal about it, you could use 2 zip ties -- one around the cable, perpendicular to its length, and the other going from the standoff through the first zip tie. Then you've got no angles and no bite.

Or slather the whole thing with electrical tape. :laughing:

Seriously though, I just looked at 334.30, and you're OK with cable ties, but it would be the inspector's call if you have them installed "so as not to damage the cable". Or if you need them at all.
 

· Registered
Joined
·
3 Posts
Discussion Starter · #8 ·
Everyone, thanks for posting. To be clear, the stand off's are 300.4(d) compliant. All that does for me is "protect cable when closer than 1.25" to the face of framing". The box the stand off's came in state that they are 300.4(d) compliant, but no mention of 334.30. It does however, also state that they "quickly secure multiple cables". My problem with thinking that they comply with 334.30 is that 334.30 states that cable running horizontally through framing is considered "secured" but, vertically it is not. Honestly, the cables are just as loose in the stand off's as they are in bored holes running vertical. This is why I posted, hoping for others with experience to enlighten me. :) Sorry for dragging this out. I hope you can see my reasons for concern.
 

· Licensed Pro
Joined
·
1,571 Posts
I use the stand-offs all the time when running 3 or more cables vertically along a stud. I never use zip ties and inspectors never have a problem with the installation.
 