I'm renovating my kitchen, and on the permit, the building official notes that the dishwasher and food disposal unit

"must be on two separate circuits of 20A each"

Does the code allow me to hook up any other recepticles on the same circuit as the appliance as long as the two appliances are not together on the same circuit? Or does "separate" really mean "dedicated"? 20A dedicated for each appliance sounds like overkill and I'd like to put more recepticles on those circuits as I'm quickly using up space in the breaker box.

I know I could go down to city hall and ask them personally but that's a hassle and just thought I'd ask you guys if this is a code requirement. What is commonly done in this situation?

Thanks!
 

· Licensed Electrician
Joined
·
4,352 Posts
From what the inspector is saying, you need to install a separate 20A circuit for each appliance.

This is not a NEC requirement. This would be a local amendment to the NEC.
 

· Electrical Contractor
Joined
·
1,995 Posts
Sometimes you can run them on a MWBC- "Multi Wire Branch Circuit". You run 12-3 on a double pole breaker and split the neutral at the junction. I kinda like this since you have to turn both off to work on one of the other. They are piped together and I like doing it that way.

Of course you should check with the local inspector to see what he thinks.

You could also ask if that is a local code amendment or NEC requirement.
 

· " Euro " electrician
Joined
·
5,369 Posts
I'm renovating my kitchen, and on the permit, the building official notes that the dishwasher and food disposal unit

"must be on two separate circuits of 20A each"

Does the code allow me to hook up any other recepticles on the same circuit as the appliance as long as the two appliances are not together on the same circuit? Or does "separate" really mean "dedicated"? 20A dedicated for each appliance sounds like overkill and I'd like to put more recepticles on those circuits as I'm quickly using up space in the breaker box.

I know I could go down to city hall and ask them personally but that's a hassle and just thought I'd ask you guys if this is a code requirement. What is commonly done in this situation?

Thanks!


I know it used to be allowed on MWBC ( mulitwire branch circuit ) however a nice gotcha this part useally get quite few peoples off guard on this part is.,

A) either appalince shall not have more than 50% of circuit rating which it mean it can not be more than 7.5 amp on 15 amp circuit or 10 amp on 20 amp circuit.

B) I do not know what your local code may required a GFCI for garbage dispoal unit so that is kinda toss up on that part only your inspector will know the details.

And more and more dishwasher and garbage dispoal unit is getting more powerfull so the amp rating do creep up so a new good quality dishwasher can hit high as 12 amp so that will kill the deal with MWBC so that one reason why it have to be it own circuit ditto with garbage dispoal unit.

Now the other reason why I say seperated circuit due some of the dishwasher I know in state side can be cord et plug attachment or hard wired but the key issue is disconnecting means with cord and plug attachment that is not a issue when you work on the dishwasher all you have to do is unplug it. but hard wired verison you will need a lock out tab to keep prevent from the breaker being turn on.

The reason why lock out on the breaker due it is not in sight of breaker box.

Hope that help you with this part.

Merci,
Marc
 
  • Like
Reactions: NJMarine

· Licensed Electrician
Joined
·
4,352 Posts
Read the OP. his inspection department is requiring separate 20 A dedicated circuits.
 

· UAW SKILLED TRADES
Joined
·
4,975 Posts
I'm renovating my kitchen, and on the permit, the building official notes that the dishwasher and food disposal unit

"must be on two separate circuits of 20A each"

Does the code allow me to hook up any other recepticles on the same circuit as the appliance as long as the two appliances are not together on the same circuit? Or does "separate" really mean "dedicated"? 20A dedicated for each appliance sounds like overkill and I'd like to put more recepticles on those circuits as I'm quickly using up space in the breaker box.

I know I could go down to city hall and ask them personally but that's a hassle and just thought I'd ask you guys if this is a code requirement. What is commonly done in this situation?

Thanks!
The NEC uses the term 'individual' branch circuit for dedicated or separate. As K Buz has mentioned you need a 20 amp branch circuit to each appliance .. nothing else can be on those circuits. It has become the norm in most areas of the country AFAIK.
 

· DIY Enthusiast
Joined
·
1,131 Posts
The NEC uses the term 'individual' branch circuit for dedicated or separate. As K Buz has mentioned you need a 20 amp branch circuit to each appliance .. nothing else can be on those circuits. It has become the norm in most areas of the country AFAIK.
What is the reasoning/thinking behind these appliances being on their own dedicated circuit?
 

· Registered
Joined
·
36 Posts
Discussion Starter · #11 ·
If we're just talking about the "potential" amps they might draw, isn't that what circuit breakers are for? What is wrong with simply adding up the power needs of the two appliances and providing a circuit that can handle that much power?

Let's say the disposal draws 10A and the diswasher is rated at 8.5A. Why is a single 20A circuit not sufficient?
 

· Engineer
Joined
·
191 Posts
If we're just talking about the "potential" amps they might draw, isn't that what circuit breakers are for? What is wrong with simply adding up the power needs of the two appliances and providing a circuit that can handle that much power?

Let's say the disposal draws 10A and the diswasher is rated at 8.5A. Why is a single 20A circuit not sufficient?
Because there are dishwashers and disposals that draw more than that. Disposals also draw more amperage when people (like my wife) shove too much crap in them :laughing: Circuit breakers aren't meant to be repeatedly tripped. This will also heat up the wiring, and can potentially damage it.

Then there's the fact that the inspector "said so." :jester:
 

· Engineer
Joined
·
191 Posts
So the real reason is to provide yet another layer of redundancy for people who don't understand how electricity works. At the expense of everyone else.
Electricity is theory; nobody really "knows" how it works :laughing:

Even those that have a good understanding of electricity wouldn't want a single 20A circuit for a dishwasher and disposal.
 

· Engineer
Joined
·
191 Posts
I'm not saying put both on one line.
Why can you not put anything else (receptacle) on the line.
Why dedicated?
You didn't, but the OP did. It used to be common that the disposal was on the same circuit as receptacles (at least in Chicago.) That's the way every house I've lived in was wired (even the 15 year old house I live in now.) My wife has literally fed everything known to man through our disposal. I'm probably going to install a monster disposal next year, and will probably need to install that dedicated 20A circuit as well. :thumbsup:

Would having a disposal on the same circuit as receptacles be a big deal for most folks, probably not. I know a few folks that have a microwave on their countertop though. This could be problematic if the microwave and disposal were on at the same time.
 

· Registered
Joined
·
92 Posts
I'm not saying put both on one line.
Why can you not put anything else (receptacle) on the line.
Why dedicated?
The presence of the receptacle or any other outlets opens the opportunity for something else, like a toaster oven, microwave, coffee maker, food processor, vacuum cleaner, etc... to be plugged in and potentially overload the circuit. You may think you won't do that, but someone else including subsequent homeowners may.

There are very specific codes for kitchens.
 

· Licensed Electrician
Joined
·
4,352 Posts
I believe most, if not all, dishwashers and disposals will say in their specs to run a separate circuit or share with each other.

There is no specific code saying disposals and dishwashers have to be on their own circuit. In fact, you according to the NEC, you could put lighting on those circuits.
 

· Registered
Joined
·
92 Posts
Other than overloading a common DW/DP circuit, I can't think of any other functional reason for dedicated lines, except perhaps the dishwasher has fancy microprocessor electronics and will choke on the transients if you throw some bones to grind in the disposal...:whistling2:
 