I have rewired my house and my shop, but have never run any underground wire. A book I bought says to run it without conduit. A local electrician says to use conduit. It'll be about 25 ft. No vehicles will go over the area. I bought outdoor wire, rated to be buried. I would like another opinion.
 

·
Registered
Joined
·
2,294 Posts
I NEVER use direct burial cable but it's legal if it's 18" deep.

I've seen some in service for 50 years with no problems.

Electricians don't like it because we like access for repairs. Conduit protects the wiring and allows us to pull new wires if somthing goes wrong.

Gophers don't generally chew thru conduit.
 

·
Pro Flooring Installer
Joined
·
8,960 Posts
Discussion Starter · #5 ·
It has to be 18" deep, even if it is in conduit? Or 12" deep? . 20 amp circuit to a garage.
 

·
Banned
Joined
·
17,248 Posts
Will this be the only circuit run to the garage?
If you need more then one circuit then you are better of (required?) with a small panel - or a MWBC

!2" deep if GFCI protected before it goes into the ground - without conduit
It must still be protected by conduit where it enters & leaves the trench
 