Not for permanently installed electric heat, since it's defined as a continuous load regardless of how it's actually used. The 80% rule applies, so 1920W max on a 20A circuit. I would install a 1500W heater with a wall mounted thermostat and timer.
Not for permanently installed electric heat, since it's defined as a continuous load regardless of how it's actually used. The 80% rule applies, so 1920W max on a 20A circuit. I would install a 1500W heater with a wall mounted thermostat and timer.You can go up to 2400 watts on a 20 amp 120 volt circuit (#12 cable).