Hi,

I'll be getting this work inspected so I need to do it right. I have the simplified code book but there's no reference to a pool heat pump. The unit I have requires 240V on a min 50A breaker.
1. I have about 25ft to the unit to run so I'm assuming 6awg is ok. It needs to run outside and I can't trench it so it will be inside a conduit.
2. Any unique requirement in regards to the conduit?
3. Another assumption I'm making is that it needs a disconnect switch next to the unit similar to an AC?
4. Does the breaker need to be a GFCI breaker?

Appreciate any advice, confirmations or corrections.

thanks,

Darren
 

· Registered
Joined
·
2 Posts
Discussion Starter · #2 ·
In case someone else is wondering...

1. 6 gage is fine, mostly because of the amperage, not the length.
2. Doesn't need to be in a conduit if it's rated for outdoor, don't remember the specifc type???
3. Still unsure about the disconnect switch.
4. GFI breaker is only required if the heat pump is within 10ft of the pool.

Not sure why I didn't get a response to this since the forum seems fairly active. Is it a newbie thing? Is there an etiquette that I didn't follow?

Oh well...
 

· Registered
Joined
·
1,802 Posts
I just now am seeing this, don't know why only now.

  • Yes, #6 is ok.
  • As for the conduit above ground, dunno - why can't trench it?
  • Whether required or not, I would put a disconnect for ease of service reasons. I have had one nearby the equipment of the pools I have had and used it.
 

· Registered
Joined
·
3,855 Posts
How are you running cable to the unit without either trenching it or putting it in conduit?
You likely need some bonding between the heat pump and the rest of the pool bonding; a pro will likely know.
 