Well you really shouldn't have romex in the pipe coming out of the floor, as that would be considered a wet location. I would use a change-over to connect to some metal flex and run that.
Well you really shouldn't have romex in the pipe coming out of the floor, as that would be considered a wet location. I would use a change-over to connect to some metal flex and run that.New kitchen island in San Diego. Made from two 24" base cabinets.
Power comes up from the concrete floor in the bottom rear corner of one cabinet, the duplex power outlet is in the upper front corner of the other cabinet.
Can I just run the romex around the inside rear of the cabinets, stapling or otherwise affixing it as appropriate?
Curious as to why you consider NM run along the upper backside (inside) of a kitchen island subject to physical damage. I'm talking about that area above where items are stored, typically 2-3in below the top of the cabinet.I agree with the previous posts. The answer to your question is NO. Even in the back of a cabinet the romex is subject to physical damage and must be protected (conduit). There shouldn't be conventional romex in conduit under/in that concrete slab either.
Help me understand the recommendation. I would have a J-box for the NM coming from under the cabinet to enter - and exit with the flex to run to the outlet box. Can the J-box and the outlet box be plastic?I generally sleeve it in 1/2 Al flex.
Yes, this goes to the core of the question. The NM can even be run behind the drawers - even less chance of damage.Curious as to why you consider NM run along the upper backside (inside) of a kitchen island subject to physical damage. I'm talking about that area above where items are stored, typically 2-3in below the top of the cabinet.
I realize there can be differing thoughts as to whether romex in conduit is ok for the run to the island. I posed the question here on the forum some time back about this. It passed inspection, but was commented that some inspectors would like to see differing.There shouldn't be conventional romex in conduit under/in that concrete slab either.
It is not a question of whether romex can be installed in conduit; it can. There is no difference of thought as to whether the conduit under the slab is a wet location; it is. Romex cannot be installed in conduit outside or underground.I realize there can be differing thoughts as to whether romex in conduit is ok for the run to the island. I posed the question here on the forum some time back about this. It passed inspection, but was commented that some inspectors would like to see differing.
No jboxes, just slide a piece of 1/2" Al flex over the exposed part of the cable. Terminate the flex in the recep box.Help me understand the recommendation. I would have a J-box for the NM coming from under the cabinet to enter - and exit with the flex to run to the outlet box. Can the J-box and the outlet box be plastic?
No jboxes, just slide a piece of 1/2" Al flex over the exposed part of the cable. Terminate the flex in the recep box.The exposed length of cable does not quite reach to the outlet location - so unfortuantly I have to go to first to a j-box, then to the outlet.
Correct? Or is there a better way?
thx!
I never mentioned what you are describing and neither did posts before mine. However, if it is exposed in a storage cabinet it could be deemed subject to physical damage.Curious as to why you consider NM run along the upper backside (inside) of a kitchen island subject to physical damage. I'm talking about that area above where items are stored, typically 2-3in below the top of the cabinet.