The manufacturer's control will always do a better job of controlling the hrv than the ecobee. The ecobee can only turn it on and off.
The interlock turns the furnace fan on when there's a demand for ventilation.
I would not do a simplified install and interlock the furnace. Running the blower motor to distribute like 100 cfm of ventilation air is very wasteful especially if you have a psc/inefficient blower motor.
Interlocking the other way, only allowing for ventilation when the furnace will render the hrv ineffective in the spring and fall, when ventilation is required most.
When it's brutally cold and the furnace is running a lot, the natural stack effect is strong and if anything houses get too much air exchange. HRV may not need to run.
Take the stale air from a suitable room in the house and dump the fresh air into the return.
When the main blower is off, fresh air will find its way into the house from the return.
The interlock turns the furnace fan on when there's a demand for ventilation.
I would not do a simplified install and interlock the furnace. Running the blower motor to distribute like 100 cfm of ventilation air is very wasteful especially if you have a psc/inefficient blower motor.
Interlocking the other way, only allowing for ventilation when the furnace will render the hrv ineffective in the spring and fall, when ventilation is required most.
When it's brutally cold and the furnace is running a lot, the natural stack effect is strong and if anything houses get too much air exchange. HRV may not need to run.
Take the stale air from a suitable room in the house and dump the fresh air into the return.
When the main blower is off, fresh air will find its way into the house from the return.