I was wondering if this looks ok. I pigtailed the ground coming from the panel to the green wire that attaches to the cover of the inlet and then connected the pigtail to the G on the inlet. This leaves the body of inlet still connected to the screw on the cover with the original green wire. I don't want to double lug or put two wires under any screws since I'm pretty sure that's against code. I know there is much debate about unbonding the G and N at the generator. You can discuss that if you want as well, but I'm trying to make sure it is wired correctly first assuming that the G and N are not bonded at the gen.
Here is a pic, sorry it doesn't show the pigtail clearly. The green wire that is clearly seen attaching to the inlet body does not go to the wire nut. It is solid to the cover.
 

Attachments

· Registered
Joined
·
7,376 Posts
The wire is most likely not needed in your installation, but it's not hurting anything. The receptacle and it's mounting cover is grounded by the bare ground wire through the chassis of the receptacle itself, thereby grounding the cover and the box when attached. It's not hurting anything, it's redundant and the inspector just may like it.
 

· Electrical Contractor
Joined
·
1,995 Posts
I was wondering if this looks ok. I pigtailed the ground coming from the panel to the green wire that attaches to the cover of the inlet and then connected the pigtail to the G on the inlet. This leaves the body of inlet still connected to the screw on the cover with the original green wire. I don't want to double lug or put two wires under any screws since I'm pretty sure that's against code. I know there is much debate about unbonding the G and N at the generator. You can discuss that if you want as well, but I'm trying to make sure it is wired correctly first assuming that the G and N are not bonded at the gen.
Here is a pic, sorry it doesn't show the pigtail clearly. The green wire that is clearly seen attaching to the inlet body does not go to the wire nut. It is solid to the cover.
I would have used stainless steel screws with silicone between the siding and the box to prevent water getting behind the siding would also use silicone around the wire between the box and the siding. Duct seal would also work in place of silicone. If you silicone or duct seal the edge of the box it's a good idea to leave the bottom open in case moisture gets in there it has a place to get out.
 

· Registered
Joined
·
1,404 Posts
Discussion Starter · #4 ·
Thanks for the advice. I did silicone the side of the house and the entrance to the box. You can see some in the pic around the clamp. The screws are temporary, at least I plan to swap them out, but you know how that goes.
 

· Electrical Contractor
Joined
·
1,995 Posts
Would not be worried about moisture in the box just getting in where you put holes in the siding.
 

· Electrical Contractor
Joined
·
1,995 Posts
Yeah behind it. What I usually do is put duct seal around where the wire/conduit to through and then a little where each screw goes through. Helps prevent water from going in.
 

· Registered
Joined
·
10,386 Posts
The receptacle and it's mounting cover is grounded by the bare ground wire through the chassis (yoke; frame; mounting strap) of the receptacle itself, thereby grounding the cover and the box when attached.

When you have a metal box, a separate length (pigtail) attached to the bundle of ground wires inside, or a long enough extension of one of the incoming ground wires, must be attached to the box itself. But if a clip intended for the purpose is squashed between the receptacle chassis and the box then only one of the two, the receptacle or the box, needs a ground wire attached to it.
 

· Registered
Joined
·
1,404 Posts
Discussion Starter · #19 ·
What's confusing is I'm not sure what he means by receptacle. He said it's grounded by the bare ground wire through the receptacle. So he's saying without pigtailing the bare ground coming from the panel going under the screw labeled G on the black part(to me the black part is the receptacle) would ground the cover? Is it touching the metal cover inside the black part somehow?
 
1 - 19 of 19 Posts