I'm planning to install an above ground pool and one of my concerns now is the electrical for the filter. The requirement is 20a120v (with twistlock plug). I looked at my existing panel box, and it seems full (see attached). I've read about using tandem breaker (gfci rated), would that work? How would I find out the right size that will fit my box?

Also, I have an existing outdoor outlet in the back - which is alao gfi rated. I'm thinking to just convert it to a junction box (with an outdoor outlet - in case I will need it for electrical power tools or appliances), and then extend it closer to the pool via approved pvc for underground installation. Will that pass in the inspection?
 

Attachments

·
Banned
Joined
·
17,158 Posts
The NEC has all the info in it you need, along with your local city hall as to what is required for your area. Appliances for pools also have in the manuals the section and info for that section from the NEC printed in them.
 

·
Sparky
Joined
·
706 Posts
You appear to have 2 full size (1" spaces available at the bottom of your panel, you need a GE THQL1120GFP (20A 1P GFCI Circuit Breaker)
 

·
Registered
Joined
·
1,324 Posts
I think that there's also other NEC requirements for pools. For instance, I think all electrical devices must be farther than 5' from the pool. There can be no overhead wires, and I believe we need a disconnect within 5'.

Hopefully others will correct me if Ii'm wrong.
 

·
Registered
Joined
·
5,105 Posts
I think that there's also other NEC requirements for pools. For instance, I think all electrical devices must be farther than 5' from the pool. There can be no overhead wires, and I believe we need a disconnect within 5'.

Hopefully others will correct me if Ii'm wrong.

You are absolutely correct. The OP should study article/section 680 in the NEC before installing anything. There are many rules for pools and you must get it right the first time. This is truly a matter of life and death.

You can read the NEC for free on the Internet. :thumbsup:
 

·
Registered
Joined
·
1,324 Posts
You can read the NEC for free on the Internet. :thumbsup:
The only thing I've found free on the internet is a Draft of the 2008, and I'm not sure if it is the final version.

J.V. do you have a link to a free final copy?
 

·
Registered
Joined
·
1,504 Posts
I always find mine by searching for "michigan electrical code" and it can be found in that manner at this link:

www.archive.org/details/​gov.mi.electrical

I don't think MI has any particular amendments, although the link might still have 2005.

I put in our pool 2 houses ago and it's a distant memory, but I put it on a dedicated circuit, put a switch to shut it off at the post I mounted the GFCI outlet on, direct wired the pump off the load side of the gfci.

I used the outlet for a pool light, which plugged in and I had a place on the post to hang the transformer, from which it ran low voltage for the actual bulb.

I'm sure you'd probably have the added requirement from 2008 to use a weatherproof gfci. It will have a WR on the face.

And yep, MI still has 2005 published even though 2008 is in effect here, so be sure to look for a 2008 or a supplement your 2005 reading with a reading of the updates in 2008.
 
  • Like
Reactions: sirsparksalot

·
Banned
Joined
·
17,158 Posts
I think that we finally made the 2008 here in my area. I have both the 2005 & the 2008, but go by the latest when working on my house. Better to do it up to the latest code and make sure that the local is okay, then get in trouble adopting a newer code than they want.
 

·
Registered
Joined
·
25 Posts
Discussion Starter · #11 ·
thanks guys for your inputs. i'll probably be wiring the pool in the next few wks. i'd have to gather tools and materials first - and the permit. the estimate i had to get it thru electricoan is 1k, and i felt thats a little too much considering he'll just pop-in new breakers.

our permit is still based on 2006 ibc NJ. 18" underground via sched 40 pvc, filter has to be at least 5' away, other sockets must be at least 10' away from pool.

one thing i dont get right now, is the term bonding... any of you guys care to explain? my thoughts are just hooking up the ground wire from filter to the body of the pool, but i mit be mistaken...
 

·
Banned
Joined
·
17,158 Posts
Bonding is like handshaking, hugging your buddy. Basically it is a piece of wire as specified in either the manual of the equipment, or the rules by your AHJ at a certain awg to connect between the equipment and a ground. Keep in mind how close your neighbors are, and if you have a HOA, because they can cause your pool to become more of a headache, especially those neighbors that think they are instantly invited all the time to use it.

Also, check to make sure if you need an alarm on the gate & back door, which is usually mandated in insurance policy. With wifi cams being cheap now days, I would get one and set it up to alert you if any activity, especially with the iPhone, there is a app called iCam, which works with multiple cameras. Good luck and let us know how things go.
 

·
Registered
Joined
·
25 Posts
Discussion Starter · #13 ·
Techy said:
You appear to have 2 full size (1" spaces available at the bottom of your panel, you need a GE THQL1120GFP (20A 1P GFCI Circuit Breaker)
is there a 20a tandem breaker for ge?
 

·
Registered
Joined
·
25 Posts
Discussion Starter · #14 ·
gregzoll said:
Bonding is like handshaking, hugging your buddy. Basically it is a piece of wire as specified in either the manual of the equipment, or the rules by your AHJ at a certain awg to connect between the equipment and a ground. Keep in mind how close your neighbors are, and if you have a HOA, because they can cause your pool to become more of a headache, especially those neighbors that think they are instantly invited all the time to use it.

[\QUOTE]

is it true that i need 8' grounding/bonding rod for the pool, filter or lights?
 

·
" Euro " electrician
Joined
·
5,369 Posts
Nope.,

If you read the NEC code art 680 this is covered very well but be aware there is early verison and later verison { 2005 or before is early while 2008 and later is later verison }

Plus the local/ state code may add to this so review it and talk to the inspector they will recomend few items along the way.

Merci.
Marc
 
  • Like
Reactions: gregzoll

·
Lic Elect/Inspector/CPO
Joined
·
369 Posts
In NJ certain areas have there own requirements. Where in NJ are you located, If you wish you can pm me for any questions.
 

·
Licensed Electrical Cont.
Joined
·
7,829 Posts
the estimate i had to get it thru electricoan is 1k, and i felt thats a little too much considering he'll just pop-in new breakers.
I think you are downplaying the significance and scope of this job to justify your unwillingness to pay a professional to do the job right.
If you are able to learn how to do this job with no mistakes or future problems that is fine, but do not belittle the role of someone who knows what they are doing.



is it true that i need 8' grounding/bonding rod for the pool, filter or lights?
Not now, not ever.
Folks who sink ground rods for pools don't know what they are doing.
 

·
Licensed Electrical Cont.
Joined
·
7,829 Posts
In NJ certain areas have there own requirements. Where in NJ are you located, If you wish you can pm me for any questions.
So how does this help the rest of the board to learn? :(
 

·
Lic Elect/Inspector/CPO
Joined
·
369 Posts
In some areas wiring to above ground pool has to in in conduit from panel to pool outlet, while other areas will allow romex from panel to outside wall of house and than conduit to pool outlet.
 

·
Licensed Electrical Cont.
Joined
·
7,829 Posts
In some areas wiring to above ground pool has to in in conduit from panel to pool outlet, while other areas will allow romex from panel to outside wall of house and than conduit to pool outlet.
And unfortunately in some areas inspectors make things up, while others will actually provide substantiation for their requests.

Honestly, this is one amendment I have not heard much of. Most places that I have seen/heard are in line with the NEC on this, excepting Chicago of course. :laughing:

As usual, it is best to check with your local AHJ.
 