I am confused. We had a frestanding electric range in our kitchen and when we cahnged the counter top to granite we switched to a Cooktop and an under counter oven and broiler. The range was on a 240 volt 40 amp circuit breaker with #8 three wire. No ground just red, black and a white neutral. The cooktop I purchased has also four burners and three of them are 1800 watts and one is 1200 for a maximum of 6600 watts. It say it needs a 40 amp circuit breaker The oven is 2000 watts and the broiler is 3000 for a total of 5000 and it says it needs a 30 amp breaker.
They now say I need two 240 wires for the new units instead of one like the range used. There is no way I can run another #8 wire because my downstairs is finished. I did have a 30 amp circuit available but it has #10 wire instead of #8 that I have redirected to the oven cabinet.
So I have a 40 amp #8 wire available and a 30 amp #10 wire available and I need to findout if I can get by with those wires since the pigtails to both the cooktop and Oven/broiler only have #12 wire in them.
Is there someway I can get by with what I have available with some combination of the two?
They now say I need two 240 wires for the new units instead of one like the range used. There is no way I can run another #8 wire because my downstairs is finished. I did have a 30 amp circuit available but it has #10 wire instead of #8 that I have redirected to the oven cabinet.
So I have a 40 amp #8 wire available and a 30 amp #10 wire available and I need to findout if I can get by with those wires since the pigtails to both the cooktop and Oven/broiler only have #12 wire in them.
Is there someway I can get by with what I have available with some combination of the two?