You only need to be 1.25 inches away from the furring strip, the depth is a non issue.
You only need to be 1.25 inches away from the furring strip, the depth is a non issue.I'm leveling a crooked ceiling in a hallway in an old rowhome using 1x3 furring strips. As part of the project I would like to remove a ceiling fan/light combo and replace with three fixtures.
The three fixtures will be in a line centered directly over a stair railing and spaced about 12 inches apart. My question is regarding the wire I will run to connect the 3 ceiling boxes. Due to the location of the rafters it would be difficult to bury the wires behind the original substrate. Am I able to run the wires in the bay between the furring strips and the new ceiling? Or is this not enough depth to protect the wire?
With 1x3 furring strips he will only have a 3/4" space to run the cable.You only need to be 1.25 inches away from the furring strip, the depth is a non issue.
I was assuming he was running parallel with the furring strips.With 1x3 furring strips he will only have a 3/4" space to run the cable.
Run the wire in notches in the furring strips and protect with metal nail plates.
I guess we are both right. Nail plates if running thru furring, nothing if running with furring.I was assuming he was running parallel with the furring strips.
Yes, that's correct.Thanks for the replies. I am running the wire parallel to the furring strips. I'm new to electrical so I want to make sure I'm interpretting the code and your responses correctly. So if I run the wire so that it is at least 1.25 inches away from the furring strip this is OK (even though there would be very little clearance between the wire and the new ceiling)?