#14 with a 25A breaker.What size wire do I need from the breaker to a 240VAC, 1.5hp deep well pump?
Motors do not have to follow this basic rule found in 240.4(D).electures.....your wire to ampacity rating is incorrect.
10 is for 30 amp
12 is for 20 amp
14 is for 15 amp.
:whistling2:Motors do not have to follow this basic rule found in 240.4(D).
People try to be helpful (and learn) here. There's no need for sarcasm. Missouri was politely corrected, and it should end that way.:whistling2:
I didn't know that that modicon meant sarcasism. I used it because I agreed with Speedy Petey. Sorry if I offended anyone. Maybe the modicans should be listed and labeled.People try to be helpful (and learn) here. There's no need for sarcasm. Missouri was politely corrected, and it should end that way.
Yeh I know how you feel. I thought I was wrong once, but I was mistaken.. (Sound fimiliar Petey?)For the record.....I'm not offended and thanks for the heads up on the code reference. I unfortunately am not correct 100% of the time.