Why 1-1-1-3 cable for copper? Standard SER cable (THHN) will let you use the 75 degree rating and then 3-3-3-5 will be sufficient. My understanding is that 60 degrees is required to be used only if the cable is to be buried in insulation. While your run is short working with those thick cables and wires is always a pain.
There appears to have been an iteration of NEC that required 60 degrees, but then later that was relaxed to require 60 degrees for cable buried inside thermal insulation only.
There appears to have been an iteration of NEC that required 60 degrees, but then later that was relaxed to require 60 degrees for cable buried inside thermal insulation only.