I'm installing an oven in a remodeled kitchen and just noticed that although the 2 hot wires are 6 gauge there is no neutral and the ground is bare and only what looks like 10 gauge. Is this a problem? I know the loads are balanced but do I need to pull a new cable or a separate bigger neutral/ground? Thanks for the help!
 

· A "Handy Husband"
Joined
·
15,062 Posts
How many conductors are in the whip for the oven?
The only acceptable three wire cable with a bare neutral/ground for a 120/240 volt appliance its SE cable originating a main panel.
Based on the poster description, the cable sounds like 6\2 NM. This cable never was a compliant install.
 
  • Like
Reactions: brric

· Registered
Joined
·
3 Posts
Discussion Starter · #6 ·
Thanks, it is a 240v circuit originating at the main panel. The new oven/micro combo has a 4 wire whip but instructions showing white and green from oven to bare,white or green wire in the existing circuit. This make sense?
 

· Registered
Joined
·
3 Posts
Discussion Starter · #8 ·
Thanks all for the help. I traced the cable and it seems that 6/2 SE was run from the panel to the original spot for the oven/range combo maybe 15 years ago when the house was built. The reno moved the new oven/micro combo to a new wall, about 10 feet. There is an accessible junction where they connected the new 6/2 NM to the existing 6/2 SE. The new 10' cable runs behind the wall of the new cabinets and would be a real pain to replace. Can i leave it or do I have to replace? Thanks for all the great help!
 

· A "Handy Husband"
Joined
·
15,062 Posts
Thanks all for the help. I traced the cable and it seems that 6/2 SE was run from the panel to the original spot for the oven/range combo maybe 15 years ago when the house was built. The reno moved the new oven/micro combo to a new wall, about 10 feet. There is an accessible junction where they connected the new 6/2 NM to the existing 6/2 SE. The new 10' cable runs behind the wall of the new cabinets and would be a real pain to replace. Can i leave it or do I have to replace? Thanks for all the great help!
It needs to replaced. You have 2 violations:
Although 3 wire installations(the SE cable) are grandfathered, they cannot be relocated or extended.
2 wire with ground NM cable was never approved for that application.
 