Discussion Starter · #1 ·
Kitchen has an island. Island has an outlet on one end. Wiring for outlet comes up from floor, through bottom of cabinet, to the blue plastic box on the side of the cabinet. Wire is covered with blue ribbed tubing, assume Carlon nonmetallic tubing conduit, like this:


Would like to add another outlet on the opposite end of the island. The drawers do not bottom out against the back of the cabinet; there's about 5" of clearance behind when they're closed. Assume no problem with just connecting a section of romex from the existing outlet to a new one on the other end, running the wire behind the drawers. Would the wire need to be mechanically supported, or could it just be run on top of the drawer slides? Would it need similar conduit?
 

· A "Handy Husband"
Joined
·
15,062 Posts
NM cable only needs to be protected from damage if it is subject to damage. The location described is not subject to damage. Secure the cable to the cabinet above the drawer slides.

Sent from my RCT6A03W13E using Tapatalk
 
  • Like
Reactions: chetwisner

· Registered
Joined
·
14,584 Posts
Discussion Starter · #6 ·
Before anyone asks, the slide design is such that the moving rail (attached to the drawer) is covered top and bottom by the static rail (attached to the cabinet frame), so "smurf tube" resting on the rail would not be subject to any friction.
 

· Registered
Joined
·
14,584 Posts
Discussion Starter · #10 ·
Had one other question before I actually get into this project. Current outlet is 15A
(actually all kitchen outlets are 15A), so I assume the house was built before 20A circuits were required by code.

If pulling a new wire off an existing outlet, is it required to upgrade the circuit to 20A?
 

· A "Handy Husband"
Joined
·
15,062 Posts
Are you sure you fo not have 15 amp receptacles on 20 amp circuits? That is compliant and the most common arrangement.

Sent from my Moto E (4) Plus using Tapatalk
 
  • Like
Reactions: huesmann

· Super Moderator
Joined
·
18,333 Posts
You can have 15 amp duplex devices on a 20 amp circuit. It it when you only have 1 spot to plug into that the receptacle needs to be 20 amp rated.
 
  • Like
Reactions: huesmann

· Registered
Joined
·
14,584 Posts
Discussion Starter · #13 ·
Well, looks like you guys are right! Checked the fuse panel and (if the PO's—or their electrician's—notations are to be believed) they're 20A circuits to the kitchen, i.e. breakers noted as kitchen are 20A. Would I use 12g wire or 14g to extend a circuit to a 15A outlet?
 