Did you put the access door back on the furnace to engage the door interlock?
Yes, I did. At least, I thought that the panel was all the way closed. After it didn't work, I ended up putting the old thermostat back in place.Did you put the access door back on the furnace to engage the door interlock?
I guess that I am a bit confused. I thought the C wire was to give 24V to provide power to the WiFi thermostat. At least that is what the install instructions for the thermostat seemed to be indicating. If that is the case and R is 24V, then a voltage potential between R and C would be zero.That "extra" wire could also have been broken or damaged as well. If you have 24 at C and R at the furnace board with the interlock switch pushed in, then see if you have it at the stat, if not it's either damaged or there's possibly another junction in between where they didn't bother carrying that wire through to the thermostat.
CC
Yeah, they don't explain it well. It took me a while, too.I guess that I am a bit confused. I thought the C wire was to give 24V to provide power to the WiFi thermostat. At least that is what the install instructions for the thermostat seemed to be indicating. If that is the case and R is 24V, then a voltage potential between R and C would be zero.