I would like to have a deeper understanding of how the current is flowing. In this case, is ground wire action as neutral?
here ya go.
That's it, no neutral. Now, if you are paying attention, then you are probably wondering "If there isn't a neutral wire then how is the circuit completed?" The answer is that when one hot wire is negative, then the other is positive, so the two hot wires complete the circuit together because they are "out of phase". This is why 240 volt circuits connect to double pole breakers that are essentially two single pole breakers tied together. In the main panel, every other breaker is out of phase with the adjoining breakers. So, in essence 240 volt wiring is powered by 2 - 120 volt hot wires that are 180 degrees out of phase.
http://www.nojolt.com/Understanding_240_volt_circuits.shtml

I am not an electrician but i think he may be wrong on the 180 degrees. but that is the layman example.
 

·
Registered
Joined
·
20 Posts
Discussion Starter · #6 ·
Let me restate this to make sure I understand. The difference in sine wave amplitude between ground and hot is 120V. The difference in sine wave amplitude between two out of phase hots is 240V. Is this correct?
 

·
Super Moderator
Joined
·
23,568 Posts
Let me restate this to make sure I understand. The difference in sine wave amplitude between ground and hot is 120V. The difference in sine wave amplitude between two out of phase hots is 240V. Is this correct?
Correct, sort of.

The measured voltage is 120/240. The actual sine wave peak to peak amplitude is more like 170/340 volts.
 

·
Licensed Electrical Cont.
Joined
·
7,829 Posts
In a typical residential 120/240V service, a 120V load is a line-to-neutral load. A 240V load is a line-to-line load. A 120/240V circuit is both. Ground has nothing to do with the functionality of the circuit.

What you have is a 240V circuit using "2-wire" cable, probably 10/2. In this case BOTH the black and white are hot, or line, conductors. A 240V circuit does NOT use a neutral.
 