Discussion Starter · #1 ·
I have a Carrier heat pump (model 38YCC030340) and a Carrier air handler (model FA4ANF030). It currently has a honeywell thermostat that has OFF-HEAT-COOL-EM. HEAT options. I want to replace it with one that has those four options plus an AUTO feature. I want the AUTO feature so I can set the upper temp for the AC to go on and a lower temp for the heat to go on without having to worry about switching it from HEAT to COOL or COOL to HEAT.

I am interested in the FocusPRO line. The models whose model numbers look like TH5XXXXX. I do not need it to be programmable, but I do want it to be digital. The problem I am having is I don't know how many heat and cool stages my units have. I know the TH5220D1029 is for 2 heat and 1 cool, TH5220D1003 is for 2 heat and 2 cool, and TH5320U1001 is for 3 heat and 2 cool. How many heat and cool stages does my Carrier heat pump and air handler have? and which thermostat is right? I am also open to other thermostat brands.

Thanks.
 

·
Administrator
Joined
·
42,396 Posts
Your heat pump is single stage.

But, your air handler could have 2 stages of electric heat.
There ain't that much of a price difference between the Th5220 and the TH5320.

So get the TH5320, and your covered.
 

·
Registered
Joined
·
15 Posts
Discussion Starter · #3 ·
So I assume that it doesn't matter how many stages the thermostat is designed for. True? I assumed that you needed to match up the thermostat based on the number of stages the heat pump and air handler have.

What the difference between the thermostats is?
 

·
Administrator
Joined
·
42,396 Posts
Stat just needs to support the number of stages of heat you have. If it has more, no problem. It just won't use the extra ability, because you tell it how many stages your equipment has. When your in installer set up.

The 2 heat 1 cool, will have a W1 and W2 terminal, and a Y terminal.
The 2 heat 2 cool, will have a W1 a W2 terminal, plus a Y1 and a Y2.
The 3 heat, 2 cool. Just has an additional terminal marked W3.
 

·
Registered
Joined
·
15 Posts
Discussion Starter · #6 ·
For a few bucks more, it makes sense to get the TH5320U1001 even though I won't use the extra stages. I know that the heat pump has heat strips and that the air handler also can supply emergency heat. So I guess that means that I have 2 heat and 1 cool stages. So I will use the W1 and W2 and Y1 and the other W's and Y's will be unused. I will verify the current setup with the thermostat that is there which is also a honeywell, but without the AUTO mode.

Anything else I should know about changing the thermostat? I plan to turn the power off to the heat pump and air handler, switch out the thermostat, and then turn the power back on. And yes, I will mark the wires that are there before I disconnect the current one.
 

·
Administrator
Joined
·
42,396 Posts
Actually.
It would be W2 and W3 for heat pumps with aux heat.
On the TH5320, W1 is also the O/B terminal for heat pumps. So its not used for aux heat. Read instructions carefully before installing.
 

·
Registered
Joined
·
624 Posts
TH5220D1029 = 2 heat 2 cool large display
TH5220D1003 = 2 heat 2 cool small display

Whatever you choose, I recommend the larger display. It will end in 1028 or 1029. I probably have these stats on a shelf in my van now. The 22 in the model number indicates 2 heat/2 cool. That TH5320 would allow for a 2 speed heatpump upgrade in the future.
 

·
Administrator
Joined
·
42,396 Posts
Heat pump stages. Refer to how many stages the heat pump itself has.
And in your case. Yes, 1 heat, 1 cool.

Aux, and emergency heat, are not stages of the heat pump.
 

·
Registered
Joined
·
15 Posts
Discussion Starter · #13 ·
Finally got to hooking this up

It is over a month later and I am finally getting to hook this up. I bought the TH5220D1003. I have it hooked up and the heat and cool work correctly. However, it seems the heat is lukewarm. With the previous thermostat I know it was warmer because I turned on the heat two nights ago and it was working well and generating more heat. Here is the difference. I have configured the thermostat to 1H/1C with no Aux heat. There is no setting in the thermostat for 1H/1C with Aux heat. In the old thermostat, the E and Aux were jumpered together and the White wire going to them. The next best configuration setting on the thermostat is for 2H/1C with Aux heat. The installation manual for a 2H/1C heat pump system indicates Aux (Auxiliary heat relay) and E (Emergency heat relay) with a note that a field jumper should be installed between Aux and E if there is no emergency heat relay. Since my old thermostat had the jumper between E and Aux, could it be that they were using emergency heat as auxiliary heat or as the second heat stage? I think I am going to change the configuration on the thermostat to 2H/1C with Aux heat and put a jumper between E and Aux (like it was on the old thermostat). But will wait until later today to see if I hear from anyone on this forum.

Side note: in the installation manual for 2H/1C heat pump systems, it does not indicate the use of W2 for anything.
 

·
Administrator
Joined
·
42,396 Posts
Thats because W2 and Aux. Are the same terminal. And it tells you to connect Aux heat to the Aux terminal.

Set up function.

1-5
2-0
3-1
5-3
6-3
7-3
8-3
9-3
12-your choice
14-0(for fahrenheit)
15-5
26-0 for comfort, 1 for economy if you don't mind being a little cooler when it gets cold out
27 leave at default
28 leave at default
 

·
Registered
Joined
·
15 Posts
Discussion Starter · #15 ·
For the cycle rates (setup functions 6 to 9), does that just control how many times the unit will turn on and off in an hour?

BTW-everything seems to be working fine. Thanks for he help.
 

·
Administrator
Joined
·
42,396 Posts
To an extent yes.

The CPH is only accurate at 50% load(50% of your systems capacity to heat or cool the house). As it gets colder or hotter out.
It will do more or less cycles.

CPH is both a timing and temp difference algorithm(but not a lot of temp difference swing).
 

·
Registered
Joined
·
15 Posts
Discussion Starter · #17 ·
Off the top of my head I cannot remember what it is set at, but I am quite sure I left them at the default setting which is 5-5, 6-5, 8-9, 9-3, 10-3 (there is no 7).
5 is heat cycle rate
6 is second heat cycle rate/aux heat
8 is emergency heat cycle rate
9 is compressor cycle rate
10 is second stage compressor cycle rate
 

·
Administrator
Joined
·
42,396 Posts
Oooops, 7 is only on the 5320 model.

5 CPH is too many for a heat pump. Waste a lot of electric. Takes too long for a compressor to get to its full efficiency.

You'll find better efficiency at 3 CPH of all heat and cool CPH on a heat pump.
 

·
Registered
Joined
·
15 Posts
Discussion Starter · #20 · (Edited)
I wasn't able to change from the default settings until last week because the house is out of state. Those default cycle rate settings managed to get me a $120 electric bill. The previous month was $20.

Another question I had was how come the manual says the heat cycle rate should be 9 for electric furnaces, emergency heat, and second stage heat/aux heat? Is a heat pump considered an "electric furnace"?

Also, what would happen if I changed the heat cycle rate from 3 to 2?
 