We have a Trane furnace xe 80 which stopped working now. It it the thermal protection device which needs to be replace. Where I can buy this part, and how much it generally cost? Very much appreciate your advice.
 

·
Master General ReEngineer
Joined
·
9,793 Posts
Ayuh,.... Is it the type that cuts the power, or the fuel,..??

Donno if the big box stores carry 'em, or not,...

If it's the electrical cut-off, 'bout any commercial Hvac supplier, or Electrical supplier oughta have 'em, in stock,...

If the fuel shut-off, the Hvac supply house would be the place to look...
 

·
Registered
Joined
·
1,796 Posts
How do you know it's not working?
Is it a main limit or a roll out switch?
An HVAC supply house that carrys Trane might be a starting point.
 

·
Registered
Joined
·
1,662 Posts
Could you post a picture of it? There are several types of thermal cutouts on the market. Some are even resettable
 

·
Administrator
Joined
·
40,292 Posts
Find out what cause it to go bad. thermal limits on a furnace are safeties, not operating limits. So there is a problem that caused it to go out.
 
  • Like
Reactions: ying

·
Registered
Joined
·
2 Posts
Discussion Starter #7
The heating system stopped working. Then checked and the diagnosis box shows "thermal protection device needs to be replaced".
 

·
Administrator
Joined
·
40,292 Posts
The heating system stopped working. Then checked and the diagnosis box shows "thermal protection device needs to be replaced".
The cause of its failure needs to be found and corrected.
 