I'm runing wire 200ft. to a new box then I will have #12wire to a 120v motor with 17amps. and #10 wire to a water pump 220v. with 7amps. off of this box .What size wire is needed for this 200ft. run?
 

·
Electrician
Joined
·
39 Posts
As dmx said, #10 Cu would be the bare minimum.

That 5% is the maximum VD recommended for the entire circuit, feeder and branch circuit combined. It's 3% recommended maximum for just the feeder.

I would recommend at least #8 or #6 Cu. It would give you a little more wiggle room should you need to add another load or change to a different motor.

The larger wire may also help as the motors age, and take more current to start up.
 