Discussion Starter · #1 ·
My house has 400amp service (not really sure why, but it does). At the main panel I have two circuits which feed our two HVAC units, one runs to our electric range, one for our dryer, and then there are two 70amp breakers for subpanels which handle everything else in the house.

The subs are old and the ground and neutrals bonded. Half of the house isn't grounded, etc. so I wanted to update everything. Contacted a local electrician and told him I planned to install two 100amp subs in place of the 70amp subs. He told me that #4 copper would be sufficient for this, but the more I'm reading I'm getting some mixed results on if that is accurate. The run from the main to the sub is just shy of 40'.

So, to summarize, is #4 copper too small for feeding a branch from the main to a sub 40' at 100amps?
 

· Registered
Joined
·
8,181 Posts
My house has 400amp service (not really sure why, but it does). At the main panel I have two circuits which feed our two HVAC units, one runs to our electric range, one for our dryer, and then there are two 70amp breakers for subpanels which handle everything else in the house.
What is the bus rating of the subpanels? Is it 70A or is it larger? Coz 70A busing is fairly rare. I would expect 100-125A busing.

Are the subs a scary-dangerous type like Zinsco or Federal Pacific?
An obsolete type like Pushmatic or really old GE?

If the panel takes modern breakers, and has 100A busing, and has enough spaces for you, I see no earthly reason to replace it. Replacing a panel is stupid amounts of work, and paying to do it merely because of the word “old” is like buying a MacBook pro and throwing it away. Naturally an electrician will do everything in his power to make you give your money to him instead of the Apple store. So I’m sure the electrician is singing songs about how much better it’d be to do it “right”.





The subs are old and the ground and neutrals bonded. Half of the house isn't grounded, etc. so I wanted to update everything.
As of NEC 2014, you are allowed to simply retrofit ground to anywhere that doesn’t have it. That is super easy to do in conduit, which you say you have.

If the conduit is metal and non-flexible, the metal conduit is a valid grounding path, so all you need to do is yank the N-G bond and yer done.

Contacted a local electrician and told him I planned to install two 100amp subs in place of the 70amp subs. He told me that #4 copper would be sufficient for this, but the more I'm reading I'm getting some mixed results on if that is accurate. The run from the main to the sub is just shy of 40'.
I suppose you can “nuke it from space” and start over, if cost is no object.

But the #1 mistake made with subpanels is getting too-small subs. Get one that is “just big enough” and you’ll have an expensive problem when you want to expand later. (That problem works out nice for electricians). As such, watch your electrician like a hawk: he will probably aim to leave you only 1-2 extra spaces. You want the panel to be about half full when the electrician is finished, and not depend on any “double-stuff” breakers (twin, tandem, quadplex etc.)

Also watch that the electrician doesn’t try to fill your panel with expensive AFCI/GFCI breakers you don’t need because you are grandfathered. (Although they can be nice for fault detection on old wiring).


So, to summarize, is #4 copper too small for feeding a branch from the main to a sub 40' at 100amps?
Yes, it’s too small for feeder. Feeder does not benefit from the 83% derate found in NEC 310.15(B)(7), which means 4 is allowable as service wire but not feeder at 100A. Note that copper THHN/THWN in conduit must use the 75C column of Table 310.15(B)(16). That is because the terminations at breaker and panel are 75C.

#4 copper is alowed For Services & feeders for residential
They’re allowed at 100A for services but only 90A for feeders. The difference is discussed in NEC 310.15(B)(7).


Why should it be stranded?
Because solid #6 and solid #4 do not exist :)


Sorry for my ignorance in terminology, but is the wire running from the main to a sub considered a feeder?
Yes. Feeder is wiring between panels.

Service wire is wiring between the meter and the first disconnect. However if the feeder acts like service wiring, in the sense that it carries 100% of the load of the service, i.e. between pole/disconnect and house... then it is allowed to use the 310.15(B)(7) derate.

There is also an exception for “feeder acting like service wire” that is tapped, e.g. if you have #4 to from your pole/disconnect to your house, then you add a 30A breaker to feed #10 wire from pole to a new shed, that doesn’t suddenly disqualify the house run for the derate. However this doesn’t help you in the slightest.
 

· Registered
Joined
·
8,116 Posts
Electricity is the movement of electrons. Electrons all repel each other because they are charged the same. That makes them travel on the outside of the wire. Stranded has more surface area, so it can carry a little more juice.
 
  • Like
Reactions: gilliger

· Registered
Joined
·
74 Posts
Discussion Starter · #15 ·
Thanks so much for the quick and detailed response. The panel that has already been replaced was an old GE from what I could tell, but I wasn't 100% sure. Couldn't find any markings or anything anywhere to confirm. The other panel is a Challenger brand and I know those have been known to have some issues.

The sub that I installed was rated at 200amps, I just de-rated it at the main with a 100amp breaker. Sounds like I need to replace that 100amp with a 90 and I should be alright from what I'm reading. I actually have other use for the 100amp breaker anyway.

Really appreciate all the feedback.
 

· Registered
Joined
·
8,181 Posts
The old GE may have been unsupportable. The Challenger panel is tip-top. The issue with Challenger is the breakers are inherently defective, but that’s trivially fixed by swapping the breakers for Eaton/Bryant BR, which are cross-listed for Type C.

Very coarsely, BRyant bought the troubled Challenger line, tossed the breakers and made their own, decided the busing was fine and kept it. They renamed the bus “BR” so they could disallow the defective type C breakers in their panel. BR breakers are cross-listed Type C, because they are the cure for Challenger disease.

So yeah any BR breakers now in there can be kept, any Challenger or older breakers, swap em for Eaton BR and boom. Save the cost of a panel swap.
 

· Registered
Joined
·
74 Posts
Discussion Starter · #18 ·
#4 copper is only rated for 85 amps. You need # 3 copper. Have you considered aluminum SER?
We already had the #4 run, so no on the aluminum.

This is where I am getting confused. Using a table in my copy of UGLY'S which is referencing NEC Table 310.16 shows 85 rating for "directly buried."
What we have is conduit run through the crawlspace from the main.

Also, doesn't 310.15(b) say that 4-4-4-6 copper is good for 100 amps to a sub panel?
 

· Registered
Joined
·
8,181 Posts
#4 copper is only rated for 85 amps. You need # 3 copper.
Good catch, yeah I misspoke. #4 is good for 85 amps. But since they don’t make 85A breakers, you get to round up to the next available breaker size, 90A.

I would do that instead of pulling all new wire just for another 10A. Er, 15A.

Have you considered aluminum SER?
OP is in conduit.
 

· Registered
Joined
·
74 Posts
Discussion Starter · #20 ·
Good catch, yeah I misspoke. #4 is good for 85 amps. But since they don’t make 85A breakers, you get to round up to the next available breaker size, 90A.

I would do that instead of pulling all new wire just for another 10A. Er, 15A
Makes sense to me, thanks! I didn't realize that about the rounding up on breakers. Confusing to a newbie like me.
 