What circuit protection needed for each of these?

1302 Views 4 Replies 4 Participants Last post by  SD515
New master bedroom and closet addition - existing master bath and closet combine into larger bath, existing master bedroom becomes office/den.


Existing circuits in bath:
  • bath outlets - GFCI (existing, GFCI outlet in adjacent 2nd bathroom)
  • bath lighting - ?
These are new circuits:
  • spa tub pump - ?
  • spa tub heater - ?
  • bedroom/closet outlets - ?
  • bedroom/closet lighting - ?
Thx
Vince
1 - 1 of 5 Posts
My answers in red:

New master bedroom and closet addition - existing master bath and closet combine into larger bath, existing master bedroom becomes office/den.


Existing circuits in bath:
  • bath outlets - GFCI (existing, GFCI outlet in adjacent 2nd bathroom)
  • As long as it is receptacles only in baths, existing is OK
  • bath lighting - ? AFCI
These are new circuits:
  • spa tub pump - ? GFCI
  • spa tub heater - ? GFCI
  • bedroom/closet outlets - ? AFCI
  • bedroom/closet lighting - ? AFCI
The bath lighting cab be combined with the bedroom/closet lighting to save AFCI breakers.