What options do I have to light a closet? It's a 3'X7' closet, I was hoping to put a 4' fluorescent on the wall directly above the door, is this ok?
Banned
Code for closet lights:
4' flourescent should be OK
NEC 410.8 (2005) is now 410.16 under NEC 2008
(wording is different under 2008)
Luminaires (Fixtures) in Clothes Closets.
(B) Luminaire (Fixture) Types Permitted. Listed luminaires
(fixtures) of the following types shall be permitted to
be installed in a closet:
(1) A surface-mounted or recessed incandescent luminaire
(fixture) with a completely enclosed lamp
(2) A surface-mounted or recessed fluorescent luminaire
(fixture)
(D) Location. Luminaires (fixtures) in clothes closets shall
be permitted to be installed as follows:
(1) Surface-mounted incandescent luminaires (fixtures) installed
on the wall above the door or on the ceiling,
provided there is a minimum clearance of 300 mm
(12 in.) between the luminaire (fixture) and the nearest
point of a storage space
(2) Surface-mounted fluorescent luminaires (fixtures) installed
provided there is a minimum clearance of 150 mm
(6 in.) between the luminaire (fixture) and the nearest
(3) Recessed incandescent luminaires (fixtures) with a completely
enclosed lamp installed in the wall or the ceiling,
provided there is a minimum clearance of 150 mm (6 in.)
between the luminaire (fixture) and the nearest point of a
storage space
(4) Recessed fluorescent luminaires (fixtures) installed in
the wall or the ceiling, provided there is a minimum
clearance of 150 mm (6 in.) between the luminaire
(fixture) and the nearest point of a storage space
410.9 Space for Cove Lighting. Coves shall have adequate
space and shall be located so that lamps and equipment
can be properly installed and maintained.