Yesterday I installed a new gas water heater with a power vent. Since then, twice the relief valve opened and about two cups of water came out. Not violently, just ran out. There is an expansion and on the supply line. Any ideas?? Thank you. Alan
 

· Super Moderator
Joined
·
8,672 Posts
Welcome to the forum everyman.

What's the temperature set at? Is expansion tank set at your incoming water pressure, usually around 55-60 psi.

Could you post a picture of your set-up, thank you.
 

· Registered
Joined
·
7 Posts
Discussion Starter · #4 ·
The temp is set at about 130 degrees. It was at 140 and I turned it down to see if that helped (it did not). The expansion tank doesn't seem to have an adjustment on it. I installed it when I replaced the water heater last time, several years ago. It's rather small, a cylinder measuring eight inches in diameter and ten inches tall. It says on it "Pre-charge pressure 40 psi." Also "Water Heater Safety Tank." There's a nipple at the bottom. I'm ancient and technologically incapable of posting a picture. The tank is up high, about ten feet from the heater, and in a 3/4" copper line supplying the heater
 

· Super Moderator
Joined
·
8,672 Posts
Expansion tank on water heater should be set to your incoming water pressure. Usually around 55_60psi. Verify what yours is first. Check at any hose bib. Easy check with water pressure gage.

There is a schrader valve On bottom of expansion tank where you can add more air. You will need to turn off incoming water and relieved pressure for accurate readings.
 