I am installing a new electric wall oven (Long Island, NY). The oven has an armored cable connected to it with 16ga stranded wires. I plan to run a new dedicated circuit from the main panel box to the oven. The distance is 75' (ouch).
The installation instructions are as follows:
"Can consume up to 4000w at 240vac. Use a circuit breaker of 30amp and wire gauge #8 awg.
A 3-wire or 4-wire single phase 120/240 or 120/208 volt electrical supply is required on a separate circuit fused on both sides of the line (time delay fuse or circuit breaker is recommended). Do NOT fuse neutral. The fuse size must not exceed the circuit rating of the appliance specified on the nameplate.
The appliance should be connected to the fused disconnect (or circuit breaker) box through flexible armored or non-metallic sheathed cable.
A suitable strain relief must be provided to attach the flexible armored cable to the junction box
Note: the armored cable leads supplied w/the appliance are UL recognized for connection to larger gauge household wiring. The current carrying capacity of the conductor is governed by the temperature rating of the insulation around the wire, rather than the wire gauge alone."
I plan to run 8/3 romex (plus ground) to a 30-amp double-pole breaker.
My questions are:
1. Do I really need #8 wire? I know everyone will say to "follow the OEM instructions", and I certainly intend to. Regardless of the responses, the incremental cost is minimal compared to the risk if it is not done right. I am really trying to understand the technical justification for the specification. Seems odd to me to connect #8 wire to #16 stranded.
2. Based on the description above, is Romex acceptable? I believe yes, based on the comment "non-metallic sheathed cable". I just want to confirm.
3. What is required to "fuse at both ends"? Do I need to run the feed to a separate fuse box/disconnect and then to the oven, even if it is on a dedicated circuit?
Thanks in advance,
B
The installation instructions are as follows:
"Can consume up to 4000w at 240vac. Use a circuit breaker of 30amp and wire gauge #8 awg.
A 3-wire or 4-wire single phase 120/240 or 120/208 volt electrical supply is required on a separate circuit fused on both sides of the line (time delay fuse or circuit breaker is recommended). Do NOT fuse neutral. The fuse size must not exceed the circuit rating of the appliance specified on the nameplate.
The appliance should be connected to the fused disconnect (or circuit breaker) box through flexible armored or non-metallic sheathed cable.
A suitable strain relief must be provided to attach the flexible armored cable to the junction box
Note: the armored cable leads supplied w/the appliance are UL recognized for connection to larger gauge household wiring. The current carrying capacity of the conductor is governed by the temperature rating of the insulation around the wire, rather than the wire gauge alone."
I plan to run 8/3 romex (plus ground) to a 30-amp double-pole breaker.
My questions are:
1. Do I really need #8 wire? I know everyone will say to "follow the OEM instructions", and I certainly intend to. Regardless of the responses, the incremental cost is minimal compared to the risk if it is not done right. I am really trying to understand the technical justification for the specification. Seems odd to me to connect #8 wire to #16 stranded.
2. Based on the description above, is Romex acceptable? I believe yes, based on the comment "non-metallic sheathed cable". I just want to confirm.
3. What is required to "fuse at both ends"? Do I need to run the feed to a separate fuse box/disconnect and then to the oven, even if it is on a dedicated circuit?
Thanks in advance,
B