25,116 Posts
cozyparts.com

Very hard to find as it has a timer built into it. Recommend a new furnace as there are some obsolete parts like the gas and air flapper assemblies. Also the heat exchanger may be cracked. Need a Lennox tech with a pressure test kit to check it.
 

· Registered
Joined
·
8,922 Posts
Ahh makes sense then.
Look into a new furnace. Haven't had a pulse around here for a long time. They all failed and were ripped out. Had a over 30 in a school we took care of. They all failed at almost the same time.
Not a high point of design for Lennox.
 

· Registered
Joined
·
17,815 Posts
If the limit part of the switch is okay but it's not bringing on the fan, you can set the t-stat to bring the fan on with a call for heat as a temporary measure.

I've read about heat exchanger problems with the early pulses but they apparently were otherwise solid. lennox was ahead of it's time; they had two-speed, high-seer a/c units in the 80s as well which must have been hell to work on.
 