I've had to cut a rectanguler shape hole in the shelve.
Well there's another sink on the other side of the wall, so changing the drain in the wall is considerable work. What is wrong with using 45s to slope down from the trap to wall?Alan said:Looks like you might as well open the wall up and adjust the elevation and the horizontal arrangement of the drain. That's what I would do. I hate cutting into cabinets.![]()
No, because water seeks it's own level. Picture a piece of pipe on grade.So if the vent is 6" below the trap, and the water wants to pull on the trap water, the vent won't stop this suction?
No, like I said if the vent is below the trap arm for instance how the OP is talking about offsetting his trap arm UPWARDS to clear a shelf, the trap can siphon. It really has nothing to do with the vent.You must be worried about situations where the vent is out of code.
Per the diagram, it is allowed to have some minimal pitch. Is that correct?Alan said:
The diagram is sketched as 1/4" per foot slope. That is why your trap arm maximum length increases with pipe size. If you slope your pipe steeper, the theory is that your maximum length should decrease. Most of the time under vanities we don't have this issue with length however.Per the diagram, it is allowed to have some minimal pitch. Is that correct?
Yes, so for a 1' length with 1.5" pipe, I can have 1.5" of drop. Right?Alan said:The diagram is sketched as 1/4" per foot slope. That is why your trap arm maximum length increases with pipe size. If you slope your pipe steeper, the theory is that your maximum length should decrease. Most of the time under vanities we don't have this issue with length however.
refer to Alan's link in post #9Why couldn't the blue pipe in the picture be cut so the trap is closer to the bottom of the sink? You should then be able to connect up to the drain with some slip fittings and a 90.