Hi all, I'm looking to hear of anyone out there is familiar with this specific problem -
The issue:
4-year old 3-zone hot water baseboard Utica Boiler stopped firing last week. Thermostats seem to work, circulator pump runs and can hear the click of the thermostats when a call is made for heat on each zone. The Field Control GVD-6 damper, when set to automatic, doesnt open. I can get it to open (occasionally) by moderately wiggling the damper shaft or by switching it from auto to manual and back. this DID result in my boiler firing for the last two days, producing heat. A relative who works for a local gas utility that does repairs asked me what type of damper I had and I told him the model of the Field Control and he was the one who suggested wiggling the damper shaft. Once open, i left the damper on manual. However, subsequent calls for heat would not ignite the boiler.
I replaced the GVD-6 with a new one, at my relative's suggestion. As soon as I installed it, the behavior was the same. I can occasionally get lucky, and the GVD-6 will open, and then I will hear the boiler ignition kick in. However, it is not consistent.
To further troubleshoot, I followed the Effikal damper troubleshooting steps and jumped the yellow/orange wires on the Molex to the damper - with the damper open, and it will not fire my boiler to ignite.
I managed to get it to work just now by unplugging the molex from the damper from the Aquastat relay, and replugging it in. I heard a 'click' and then the boiler fired.
So my questions:
- Is my damper indeed good, or bad?
- Could it be the aquastat relay?
- Is it a thermocoupler or something with the ignition?
Ive had two days now where once I can get the damper in the open position (set on manual) and i manage to get the boiler to ignite, I will have heat for some period of time until it will not cycle on again. Other thing of interest: I heard a fairly low grumble/rumble yesterday when the heat was going on prior to the sound of ignition. I was upstairs and not next to the boiler when it happened, but i felt the vibration in the floor and it definitely was not a 'normal' sound that Im used to after 4 years in the house. I was thinking this might be a zone valve?? I dont know much about HVAC only what Ive been reading online and learning as I go.
Thanks for any insight!
JK
The issue:
4-year old 3-zone hot water baseboard Utica Boiler stopped firing last week. Thermostats seem to work, circulator pump runs and can hear the click of the thermostats when a call is made for heat on each zone. The Field Control GVD-6 damper, when set to automatic, doesnt open. I can get it to open (occasionally) by moderately wiggling the damper shaft or by switching it from auto to manual and back. this DID result in my boiler firing for the last two days, producing heat. A relative who works for a local gas utility that does repairs asked me what type of damper I had and I told him the model of the Field Control and he was the one who suggested wiggling the damper shaft. Once open, i left the damper on manual. However, subsequent calls for heat would not ignite the boiler.
I replaced the GVD-6 with a new one, at my relative's suggestion. As soon as I installed it, the behavior was the same. I can occasionally get lucky, and the GVD-6 will open, and then I will hear the boiler ignition kick in. However, it is not consistent.
To further troubleshoot, I followed the Effikal damper troubleshooting steps and jumped the yellow/orange wires on the Molex to the damper - with the damper open, and it will not fire my boiler to ignite.
I managed to get it to work just now by unplugging the molex from the damper from the Aquastat relay, and replugging it in. I heard a 'click' and then the boiler fired.
So my questions:
- Is my damper indeed good, or bad?
- Could it be the aquastat relay?
- Is it a thermocoupler or something with the ignition?
Ive had two days now where once I can get the damper in the open position (set on manual) and i manage to get the boiler to ignite, I will have heat for some period of time until it will not cycle on again. Other thing of interest: I heard a fairly low grumble/rumble yesterday when the heat was going on prior to the sound of ignition. I was upstairs and not next to the boiler when it happened, but i felt the vibration in the floor and it definitely was not a 'normal' sound that Im used to after 4 years in the house. I was thinking this might be a zone valve?? I dont know much about HVAC only what Ive been reading online and learning as I go.
Thanks for any insight!
JK