Discussion Starter · #1 ·
We had a contractor install a new Anderson sliding door 4 years ago and I remember him telling me he had to trim the studs to allow the door to fit in the rough opening. Currently we are remodeling our downstairs and removed the drywall and were surprised to see only single 1” wide jack studs supporting the 4x12 header above the door. There is a large second floor master bath with a mudded tile floor and a large two-person tub directly above that cantilevers out the back. I ran a string and the center of the two top plates deflects almost a 1/2” over a 6’ span in the middle. The load on this header must be substantial and even single unripped 2x4 jack studs would be insufficient for the load



I don’t see anything I can do to correct this situation except to fur out a properly sized load-bearing wall in front of the existing exterior wall. I would like to support the 2x12 floor joists above with a 4x12 Parallam. I would carry the load down to the foundation wall using 4x6 posts and building up the sill plate under the subfloor. See drawing below.



Does anyone see a problem with this approach?

Thanks for taking the time to read my post.
 

· Stay-at-home GC
Joined
·
638 Posts
Any reason not to just crib up the floor and reframe the exterior wall with the appropriate jack studs? Looks like your added work will be moving the exterior receptacle box on the left and what I assume is a vent run from the basement on the right. But you'll make up for it in cost and not having to mess with jam extensions when you are ready to trim the door. Of course I might be missing something obvious here.


Other than that my only comment might be the framing member laying sideways along the mud-sill. As it dries it will shrink. Maybe enough to allow your fur wall to sag.
 

· Residential Designer
Joined
·
1,615 Posts
Don't do any over-kill on your project unless needed. Does the header actually sag?
put your line on the top of the header and see, if it doesn't sag then your contractor may have installed that rather over-sized header incorrectly.
That he may not have braced the floor when installing the header and it fell a bit.

Andy.
 

· Registered User
Joined
·
11,730 Posts
It appears the header is straight on top, lining a straight edge in front of my monitor (not totally accurate). The plate is lower from the string line - 1/4"? Cut off the extra length of hanging string as it will help sag the main line. Try adding slightly longer cripple studs next to the existing over the headers after checking header for straight as Andy said. You will lose some elevation as mentioned due to lumber shrinkage, but not recent if done 4 years ago; http://www.paintsource.net/pages/solutions/new construction/wood_shrink.htm

See if adding the longer cripples bows the header. Add some metal gusset plates at the jacks or tear into it and add these: http://www.strongtie.com/products/connectors/HH.asp

Gary
 

· Registered
Joined
·
80 Posts
Discussion Starter · #6 · (Edited)
Any reason not to just crib up the floor and reframe the exterior wall with the appropriate jack studs? Looks like your added work will be moving the exterior receptacle box on the left and what I assume is a vent run from the basement on the right. But you'll make up for it in cost and not having to mess with jam extensions when you are ready to trim the door. Of course I might be missing something obvious here.


Other than that my only comment might be the framing member laying sideways along the mud-sill. As it dries it will shrink. Maybe enough to allow your fur wall to sag.
CplDevilDog,

Thank you for your comments.

Based on the load above and code there should be two 2x4 jack studs under the 4x12 header. The header was obviously cut too short when the building was constructed in 1984. I remember the contractor who installed the new sliding door in 2006 had a very difficult time removing the original slider because there was zero clearance in the rough opening. He had to rip the single jack studs to 1” in thickness just to obtain the minimum rough opening size for a standard 6 foot wide sliding door.

To reframe the opening properly the header must be replaced with one wide enough for two jack studs and allowance for the minimum rough opening size of the sliding door. To do this I would have to remove the stucco from the exterior of the wall, destroy the Anderson doorframe and most likely the floor and wall tile in the master bath above.

Regarding the 2x6 PT I would rip for the mudsill and the 6x6 I would place on top of it. I have both stored inside for over a year and no more shrinking will occur.
 

· Registered
Joined
·
80 Posts
Discussion Starter · #7 · (Edited)
Don't do any over-kill on your project unless needed. Does the header actually sag?
put your line on the top of the header and see, if it doesn't sag then your contractor may have installed that rather over-sized header incorrectly.
That he may not have braced the floor when installing the header and it fell a bit.

Andy.

Andy,

Thank you for your comments.

The original builder installed the header in 1984 and a 4x12 header is called out in the original drawing. There is no detail on the drawing indicating the number of jack studs, but code dictates two must be used based on the load above.
 

· Registered
Joined
·
80 Posts
Discussion Starter · #8 ·
It appears the header is straight on top, lining a straight edge in front of my monitor (not totally accurate). The plate is lower from the string line - 1/4"? Cut off the extra length of hanging string as it will help sag the main line. Try adding slightly longer cripple studs next to the existing over the headers after checking header for straight as Andy said. You will lose some elevation as mentioned due to lumber shrinkage, but not recent if done 4 years ago; http://www.paintsource.net/pages/solutions/new%20construction/wood_shrink.htm

See if adding the longer cripples bows the header. Add some metal gusset plates at the jacks or tear into it and add these: http://www.strongtie.com/products/connectors/HH.asp

Gary

Gary,

Thank you for your comments.

The plate deflection was measured slightly over 3/8” before the other string you noticed was strung. I only mentioned the deflection of the plates to emphasize the load above. This wall supports a second floor and roof load with a heavy stucco exterior. The room above is a master bath with a thick-mudded tile floor and floor to ceiling mudded tiled shower. There is also a large two-person Jacuzzi tube above the slider that cantilevers out the back over the door.

NOTE: We are in a seismic 4 area.

BTW, I only use structural select KD DF for all my 2x lumber. My lumber yard here stocks it for just pennies more than green lumber.
 

· Registered
Joined
·
80 Posts
Discussion Starter · #9 ·
You said the contractor installed a 'new' sliding door, was there something there before? Did he put that header in or just those 1" jacks?
Why 1" btw?

Tizzer,

Thank you for your comments.

We upgraded from a 6 foot wide single pane aluminum sliding door to a 6 foot wide Anderson Gliding Door. The 4x12 header is original construction and the contractor that installed the new Anderson door ripped the jack studs to obtain the minimum rough opening.
 

· Registered
Joined
·
10 Posts
If you do not want to reframe the opening, one way to reinforce the header connection would be to add an addition full height stud, add lag bolts thru the full height studs into the end grain of the header, and add a steel side plate with nails into the full height studs and side of the header.

But I like your idea better.
 

· Registered
Joined
·
80 Posts
Discussion Starter · #11 ·
I have been out of commission and not been able to get any work done or post for over a week after an eye injury and severe knee pain.

Any suggestions on the best way to tie the new 2x4 support wall to the inside corner intersection of the existing 2x4 and 2x6 stud walls?

Thanks

 

· Registered User
Joined
·
11,730 Posts
Add a 2x6 stud to the back (inside 2x6 wall) of the 4x, flush on the inside, sticking past the 2x4 wall end stud for nailing there. Use drywall clips at inside corner.

Gary
 

· Registered User
Joined
·
11,730 Posts
Possible confusing explanation. Picture a 2x6 stud nailed to the backside of the 4x6, on the 4x side, resting on the 2x6 bottom plate. It will stick out the back 2" behind the 2x4 end stud wall. Face nail it through the 2x4 left side (the right side is face nailed to the end 2x6 already holding the walls together.
Just as it sits, put a 2x6 stud in the 2x6 wall right behind the 4x6 and 2x4 next to it, tying them together. Nail the 2x6 to the post first before the plates.

Gary
 

· Registered
Joined
·
80 Posts
Discussion Starter · #15 ·
Possible confusing explanation. Picture a 2x6 stud nailed to the backside of the 4x6, on the 4x side, resting on the 2x6 bottom plate. It will stick out the back 2" behind the 2x4 end stud wall. Face nail it through the 2x4 left side (the right side is face nailed to the end 2x6 already holding the walls together.
Just as it sits, put a 2x6 stud in the 2x6 wall right behind the 4x6 and 2x4 next to it, tying them together. Nail the 2x6 to the post first before the plates.

Gary

Gary,

Thank you again for suggesting a solution. I understand the first part of what you are suggesting, but there is no way to face nail the 2x4 to the 2x6 nailed to the 4x6 unless I remove the exterior stucco and sheathing.

The last part Just as it sits, put a 2x6 stud in the 2x6 wall right behind the 4x6 and 2x4 next to it, tying them together. Nail the 2x6 to the post first before the plates.” I just can’t picture.

Howard
 

· Framing Contractor
Joined
·
1,758 Posts
We had a contractor install a new Anderson sliding door 4 years ago and I remember him telling me he had to trim the studs to allow the door to fit in the rough opening. Currently we are remodeling our downstairs and removed the drywall and were surprised to see only single 1” wide jack studs supporting the 4x12 header above the door. There is a large second floor master bath with a mudded tile floor and a large two-person tub directly above that cantilevers out the back. I ran a string and the center of the two top plates deflects almost a 1/2” over a 6’ span in the middle. The load on this header must be substantial and even single unripped 2x4 jack studs would be insufficient for the load



I don’t see anything I can do to correct this situation except to fur out a properly sized load-bearing wall in front of the existing exterior wall. I would like to support the 2x12 floor joists above with a 4x12 Parallam. I would carry the load down to the foundation wall using 4x6 posts and building up the sill plate under the subfloor. See drawing below.



Does anyone see a problem with this approach?

Thanks for taking the time to read my post.
Did you have permits and inspections 4 years ago?
 

· Registered
Joined
·
80 Posts
Discussion Starter · #17 ·
Did you have permits and inspections 4 years ago?
Permits are not required in our County for replacing windows.

I have finished widening the support on top of the sill plate in the crawlspace and now I am getting ready to work on the new support wall. I will need to shim the Parallam to the ceiling joist above since the center ceiling joist are 1/2” lower than the outer ones. I thought I would use KD DF 2x4 blocks under the center ceiling joist and progressively thicker blocks as I work my way out to the ends. I have very dry DF 3x4 I could trim to thicknesses greater than 1-1/2”. See drawing below.

 