I am buying a house. I have 125 Amp wires coming into a panel that is rated 100 amps. The house inspector said that the electrical panel should be upgraded for "proper fusing". The electrician said that the electrical panel amps and wires are installed per code and in a safe installation. My question is, is this correct and what happens if there is a electric surge as lightning. Will this fry the panel causing it to need to be changed at a later time. Also the addendum from me to the seller said that the Seller is to upgrade electrical panel to service 125 amp wires coming into the house. Can anyone help me.
 

· Licensed Electrical Cont.
Joined
·
7,829 Posts
The 100A panel is FINE, and quite typical. I highly doubt there is 125A wires coming into the house, but even if there were what would it matter??? Larger wires are almost never a problem, but too small usually is. Also, a 125A residential service is pretty rare. Typically it is 100A, 150A or 200A, with 400A becoming more common lately.

I will say, it sounds like your home inspector is pretty clueless about this stuff. Especially considering he states it should be upgraded for "proper fusing". He does not know what he is talking about, and you can tell him I said that.

The receptacles are unrelated to your panel. For older ungrounded wiring two-prong receptacles, or GFI protected receptacles are perfectly safe and legal.
 
  • Like
Reactions: szcott

· Licensed Electrical Cont.
Joined
·
7,829 Posts
Sorry if I came off as gruff. I just have a really sore spot for H-I's that call out stupid stuff. Most (potential) homeowners take this as gospel and demand things be done.
 
  • Like
Reactions: rjniles

· Electrical Contractor
Joined
·
3,370 Posts
Unless your service panel is overloaded, there is no need to obtain "proper fusing" on the incoming lines. You already have it, with your main breaker.

There is no requirement that any piece of wire be max'd out, and your so-called inspector would be hard pressed to cite a Code section that has been violated. :furious:
 

· A "Handy Husband"
Joined
·
15,054 Posts
Sorry if I came off as gruff. I just have a really sore spot for H-I's that call out stupid stuff. Most (potential) homeowners take this as gospel and demand things be done.
I agree about the Home Inspectors (use the term loosely) calling out items that are not code violations and the sellers demand to be changed.

Example:

Lack of GFCI in areas that current code calls for but not when the house was built/wired.

GFCI's that replaced 2 wire receptacles without grounds and are properly labeled. They fail to trip when they use their push button receptacle tester. (I swear that if you bootlegged the ground they would be happy.)
 