My wife and I recently had a home inspection done at a property we wanted to buy. In the 200amp box several of the 220 line neutrals were just folded up in the box and not attached to the Neutral or ground bar? The house inspector said this was a bad thing, I was an electrician for years and never saw this that I can remember. My dad was my teacher and master electrician and he is gone 20 yrs now so I can't ask him. So my question is, why would someone leave those neutrals unattached? Is it right, safe or normal.:eek:
 

·
Electrical Contractor
Joined
·
3,368 Posts
How do you know they are "220" circuits?

In the US a so-called "220" circuit does not need a neutral connection.

So, maybe they are from old circuits that have been abandoned? Maybe some electric heat circuits that are disconnected?
 

·
Super Moderator
Joined
·
16,289 Posts
Perhaps someone ran xx-3 cables an used the two hots for a straight 240 volt circuit instead of running xx-2 cable and re-identifying the white as a hot.
 

·
Super Moderator
Joined
·
22,994 Posts
Unless we know what those circuits are for we can't tell you if the neutrals folded is a bad thing. Some circuits only require 240 volts so the white wire is extra.
 

·
Registered
Joined
·
3 Posts
Discussion Starter · #5 ·
Neutrals not attached

Wow fast reply. The circuits go to the Electric furnace and then head to the heat pump. There is 3/6 with a ground. The Red and Black are attached to breakers in the furnace line in terminals. The white wire is attached in the furnace but not in the panel. It is actually 240 single phase. Hope that answers your inquiry. Your help and banter is invaluable to solve this issue.
:thumbup:
 

·
Super Moderator
Joined
·
16,289 Posts
Both of those should be straight 240 and no neutral is needed. Someone could have run xx-2 instead.

There is no safety issue or code issue either.
 

·
Registered
Joined
·
3 Posts
Discussion Starter · #7 ·
Thank you very much Jim. Just never saw it like that. My generator and other 240v circuits all have all the lines hooked up. I appreciate your help. Needed to make some sense out of this.
:thumbsup:
 

·
Licensed Electrical Cont.
Joined
·
7,829 Posts
My generator and other 240v circuits all have all the lines hooked up. I appreciate your help.
Your generator feed and some appliances are 120/240v, not just straight 240v. There IS a difference.
 
  • Like
Reactions: SW Dweller

·
Licensed Electrical Cont.
Joined
·
7,829 Posts
Perhaps someone ran xx-3 cables an used the two hots for a straight 240 volt circuit instead of running xx-2 cable and re-identifying the white as a hot.
THIS.

Some people like to waste money and run XX/3 because they think they HAVE to use black and red. They are unaware that using the white for a hot is typical and accepted.
This is unfortunate for the original installer since you said it was large 6.3 cable.
The ONLY up side is that years later if you replace the appliance with something that is 120/240v and requires a neutral it is there.
 

·
Registered
Joined
·
9,863 Posts
The white wires should not be snipped off.No wire should ever be snipped off from a cable that is modern enough and in good enough condition to be used for anything.

If the white wire is not needed and folded up in the panel, its other end should be unconnected and folded up also.

If 3 wire cable happens to be run for a 240 volt only circuit, red and black should be used and white should be folded aside.
 

·
Super Moderator
Joined
·
16,289 Posts